Low output voltage on battery mode.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Low output voltage on battery mode.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:22 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
9
10800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 AM . Last Modified: ‎2024-03-21 05:34 AM

Low output voltage on battery mode.

Hi, guys.

I'm from Brazil e I have an APC BR1200N-BR (input: bivolt / output: 120V). Some days ago I've tested the output voltage using an eletronic multimeter and, for my surprise, I've noticed that, when on battery mode, the device provides a strange too low output voltage: around 90V.

When working with input power, the reading of the output voltage is around 115V. That is to say, completely normal. However, on battery mode the too low voltage has scared me, as, I think, 90~92V doesn't seem to be a reasonable margin for devices that require 120V, although, up to now, I haven't faced any problem.

Besides that, another fact has called my attention. A friend of mine has the same unity model and he, indeed, has been having troubles. His pc reboots all the time and the motherboard, when the pc loads Windows, has stability problems and fan reading issues. In his case, the output voltage measured with the multimeter, on battery mode, is: 70~75V.

Having that said, I'd like to know what would be the accurate and safe output voltage range when on battery mode, so that the devices connected to the UPS work without risk of problems.

Thanks in advance and sorry for my bad english.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:22 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 AM . Last Modified: ‎2024-03-21 05:34 AM

Alexandre,

Are you using a non True RMS or a True RMS voltmeter? If you are using a non True RMS, that is the usual voltage that you'll get on our UPS. If you could find a true RMS voltmeters you could use that and it would give you a reading of ~115V AC.

With regards to your friends problem, it can be caused by a lot of things such as: power supply is too sensitive with the UPS transfer time, power supply doesn't read or like the step approximated sine wave that BackUPS supplies.

Below are APC Knowledgebase articles that would give you ideas with your problems:

[True RMS Voltmeter Required to Read Stepped Approximated Sine Wave|http://nam-en.apc.com/app/answers/detail/a_id/1493/kw/true%20rms%20voltmeter/session/L3RpbWUvMTMxMDk...]
[Different Types of Voltmeters|http://nam-en.apc.com/app/answers/detail/a_id/4119/kw/true%20rms%20voltmeter/session/L3RpbWUvMTMxMDk...]
[Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.|http://nam-en.apc.com/app/answers/detail/a_id/20/kw/equipment%20reboots/session/L3RpbWUvMTMxMDk2MTk4...]

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Well. If there's something I can add is that, when reading the voltage in the wall socket, the multimeter reports about 222V. That is to say, the electrical source for the UPS is completely normal.

Then, my concerns come exactly from the fact that, although I have a normal reading from the wall socket, the reading from the UPS, when on battery mode, is far too low (90V).

Thanks again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
2
10800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Like what I have said on my previous post. You will need to use a True RMS voltmeter to read the proper voltage of the UPS when it is running on battery. When our BackUPS are online, it provides whatever is being fed into it unless it is trimming or boosting the voltage. When it goes to battery mode, it switches to a step approximated/ square wave. This is where the problem happen, if you are using a non True RMS voltmeter it cannot read the voltage properly. But if it is a True RMS voltmeter, it will read all the voltage points and would tell you that the voltage is ~115V AC.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Old post but I'm having the same issue. Question if my voltmeter is reading 89V and my equipment is not working on a fully juiced battery then my equipment is faulty as well? I can't believe there was no response from the other user or they probably lost patience because of lack of attention to their issue

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

You probably are not using a True RMS meter, as mentioned. More detail is here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA157483 

The UPS outputs a step approximation to a sinewave so if you aren't using a true RMS meter, it will show as 88-90V for 120V. You will likely see 120V from the wall outlet correctly using a non-True RMS meter because it is a pure sinewave and not a step approximation to a sinewave..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Lacking a "True RMS" Voltmeter, a very effective test is to plug an incandescent (filament) light bulb (NOT LED or flourescent) into the UPS output. The brightness of the light should change very little (dimmer or brighter) when you go from utility (mains) to battery by pulling the wall plug. Not only does this tell you that the UPS is providing something close to the proper voltage, like you could read with a "True RMS" voltmeter, but it also demonstrates that the UPS can support (at least) the load created by the light bulb (100W?) which a voltmeter cannot.

You would know if you have a "True RMS" voltmeter, because they cost significantly more than your typical multimeter!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10798
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Sorry, just noticed the second part of your question about your equipment not working!

Some equipment does NOT respond well to a stepped approximation UPS output. I won't try to suggest all the possible ways that something could react if it can only work correctly on a "clean" sinewave input, but if your equipment operates correctly when the UPS is running from utility (mains) power, but doesn't function correctly (or at all) when the UPS is on battery, I would suspect it needs a better (True Sinewave Output) UPS. I am only a home user of APC products, so I can't tell you what the best choice of replacement APC brand (or other) UPS is for your needs, but I'm sure there are many options available!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

rhjt
Crewman rhjt
Crewman

Posted: ‎2023-11-15 10:58 AM

In response to BillP
0 Likes
0
8009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-15 10:58 AM

may be true, but voltage is LOW.  Lamps are dim and fans runs slower.  devices which require full voltage may not operate or even fail.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:22 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:22 AM . Last Modified: ‎2024-03-21 05:34 AM

Alexandre,

Are you using a non True RMS or a True RMS voltmeter? If you are using a non True RMS, that is the usual voltage that you'll get on our UPS. If you could find a true RMS voltmeters you could use that and it would give you a reading of ~115V AC.

With regards to your friends problem, it can be caused by a lot of things such as: power supply is too sensitive with the UPS transfer time, power supply doesn't read or like the step approximated sine wave that BackUPS supplies.

Below are APC Knowledgebase articles that would give you ideas with your problems:

[True RMS Voltmeter Required to Read Stepped Approximated Sine Wave|http://nam-en.apc.com/app/answers/detail/a_id/1493/kw/true%20rms%20voltmeter/session/L3RpbWUvMTMxMDk...]
[Different Types of Voltmeters|http://nam-en.apc.com/app/answers/detail/a_id/4119/kw/true%20rms%20voltmeter/session/L3RpbWUvMTMxMDk...]
[Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.|http://nam-en.apc.com/app/answers/detail/a_id/20/kw/equipment%20reboots/session/L3RpbWUvMTMxMDk2MTk4...]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Well. If there's something I can add is that, when reading the voltage in the wall socket, the multimeter reports about 222V. That is to say, the electrical source for the UPS is completely normal.

Then, my concerns come exactly from the fact that, although I have a normal reading from the wall socket, the reading from the UPS, when on battery mode, is far too low (90V).

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
2
10801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Like what I have said on my previous post. You will need to use a True RMS voltmeter to read the proper voltage of the UPS when it is running on battery. When our BackUPS are online, it provides whatever is being fed into it unless it is trimming or boosting the voltage. When it goes to battery mode, it switches to a step approximated/ square wave. This is where the problem happen, if you are using a non True RMS voltmeter it cannot read the voltage properly. But if it is a True RMS voltmeter, it will read all the voltage points and would tell you that the voltage is ~115V AC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Old post but I'm having the same issue. Question if my voltmeter is reading 89V and my equipment is not working on a fully juiced battery then my equipment is faulty as well? I can't believe there was no response from the other user or they probably lost patience because of lack of attention to their issue

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

You probably are not using a True RMS meter, as mentioned. More detail is here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA157483 

The UPS outputs a step approximation to a sinewave so if you aren't using a true RMS meter, it will show as 88-90V for 120V. You will likely see 120V from the wall outlet correctly using a non-True RMS meter because it is a pure sinewave and not a step approximation to a sinewave..

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Lacking a "True RMS" Voltmeter, a very effective test is to plug an incandescent (filament) light bulb (NOT LED or flourescent) into the UPS output. The brightness of the light should change very little (dimmer or brighter) when you go from utility (mains) to battery by pulling the wall plug. Not only does this tell you that the UPS is providing something close to the proper voltage, like you could read with a "True RMS" voltmeter, but it also demonstrates that the UPS can support (at least) the load created by the light bulb (100W?) which a voltmeter cannot.

You would know if you have a "True RMS" voltmeter, because they cost significantly more than your typical multimeter!

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

0 Likes
0
10799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:23 AM . Last Modified: ‎2024-03-21 05:34 AM

Sorry, just noticed the second part of your question about your equipment not working!

Some equipment does NOT respond well to a stepped approximation UPS output. I won't try to suggest all the possible ways that something could react if it can only work correctly on a "clean" sinewave input, but if your equipment operates correctly when the UPS is running from utility (mains) power, but doesn't function correctly (or at all) when the UPS is on battery, I would suspect it needs a better (True Sinewave Output) UPS. I am only a home user of APC products, so I can't tell you what the best choice of replacement APC brand (or other) UPS is for your needs, but I'm sure there are many options available!

Reply

Link copied. Please paste this link to share this article on your social media post.

rhjt
Crewman rhjt
Crewman

Posted: ‎2023-11-15 10:58 AM

In response to BillP
0 Likes
0
8010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-15 10:58 AM

may be true, but voltage is LOW.  Lamps are dim and fans runs slower.  devices which require full voltage may not operate or even fail.

Reply

Link copied. Please paste this link to share this article on your social media post.

Deoraj
Deoraj
Cadet

Posted: ‎2024-09-09 06:12 PM

In response to BillP
0 Likes
0
3505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-09 06:12 PM

What if the display on the UPS is showing an output of 60v with no loads connected after battery replacement? I did not even want to plug anything in when I saw that 60v. Input is 117v and frequency is 60Hz. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of