Is there any limit to how long an LE1200 can output 110V in an under-voltage situation that is still over 80V?
Thanks,
dbutch
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:49 AM . Last Modified: 2024-03-27 01:28 AM
Hello David,
The LE1200 uses a multi-tap transformer, so there should be no limit on how long it will operate. These tend to reach their end of life when there is a lot of switching between taps in a short amount of time, and heat or arcs create welding, but they typically last a while.
Thanks,
Shanon
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:49 AM . Last Modified: 2024-03-27 01:28 AM
Hello David,
The LE1200 uses a multi-tap transformer, so there should be no limit on how long it will operate. These tend to reach their end of life when there is a lot of switching between taps in a short amount of time, and heat or arcs create welding, but they typically last a while.
Thanks,
Shanon