ES 550 shuts down suddenly when printing a document

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • ES 550 shuts down suddenly when printing a document
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

0 Likes
4
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

ES 550 shuts down suddenly when printing a document

after working flawlessly for past 3 years, my UPS ES 550 decided to shut down suddenly today while printing a document. Worse still, is that the battery backup doesn't kick in to keep the computer running, everything goes dead together, instantly.  After I shut off and push the reset button on the UPS and then turn the computer back on, everything works fine until the next time I try to print again.  Also, would point out that until the shutdown occurs, the green light appears normally, and i have never seen any red blinking light or warning alarms to suggest the battery or unit is otherwise defective.

Before anyone says "don't plug a printer into the UPC!", I will state that the only thing plugged into the unit is the desktop computer (with standard 250 watt power supply) and my computer monitor.  The printer is plugged into a separate power outlet.

I have reproduced the situation several times, and the fault continues.  I tried switching out the ups for another unit and the problem is not occurring now... so it would appear there is something wrong with the ES 550.

Any ideas would be appreciated!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 550
  • backup
  • battery
  • es
  • no
  • shutdown
  • sudden
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

0 Likes
0
2166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

thanks for the info William, very helpful!

I would clarify re the LEDs.  the green one does in fact remain on steady while the unit is in operation, and goes out when the unit fails.  I was meaning that the red LED does not come on, either steady or blinking red, when the unit fails.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

0 Likes
0
2167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

When you mention a "reset" button, are you referring to the power switch or circuit breaker on the unit? If the UPS's circuit breaker has tripped, the problem is likely internal to the UPS.

I believe the battery within your Back-UPS ES 550 is extremely weak or bad, regardless of whether it has produced a failure alarm or not. Practical experience suggests these units are not particularly good at noticing when their batteries have failed. Even if they do, the failure state is not retained if the unit is restarted. Some older models also lack the red LED.

The printer, which I'm assuming to be a laser type, may be able to trigger enough of a voltage sag that the UPS circuitry tries to intervene and falls over due to  flat battery. This could be true even though the printer is plugged in to a different outlet, if that outlet is on the same circuit or leg of AC line power as the outlet serving the UPS.

You can test the battery with a DC voltmeter, though this cannot tell you much about the battery's ability to deliver enough electrical energy under a load. Disconnect it from the UPS for this test. A battery that has just been taken off the charger should measure anywhere between 12.5 to 13.1 volts or so, maybe slightly more or less.

Should the issue turn out to be a matter of voltage sag, it wouldn't be a bad idea to have an electrician inspect your wiring and outlets. The UPS sensitivity can also be adjusted downward, although this may require the use of PowerChute Personal Edition software on an ES model.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

0 Likes
0
2167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

Yes, im referring to the circuit breaker on the end of the unit.  I agree about your opinion that the battery may be bad.  Its been sitting there on trickle charge for several years and never been discharged (to my knowledge), so that would make sense.  The ES 550 does have the red and green LEDs, however, other than lighting briefly when you turn on the power switch, it has remained off.

Correct about the laser printer.  At the instant the fuser kicks in, the UPS kicks out.  The printer is plugged into the other receptacle on the same wall outlet as the UPS.  

I will plan on pulling the battery and checking the voltage.  In the event the battery is shot, is it reasonable to get a new battery for the unit, versus buying a complete new UPS?  I noted on the user guide that Schneider sells the replacements for it, but i haven't priced them yet.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

0 Likes
0
2167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

It's kind of odd that the LED would only illuminate briefly when you press the power switch. So long as the unit is on and line power is normal, the LED should be green and illuminated constantly.

I believe the replacement battery for your ES 550 is an APC RBC17. The genuine APC battery comes with a warranty, technical support, free recycling of your old battery and guaranteed compatibility. Its only drawback is that of cost: a totally brand new ES 550 costs only a little bit more. I don't know what APC's return policy on batteries is, should your UPS turn out to be broken.

Generic batteries are much cheaper, though not all of them are held to the same quality standards and you'd be using one at your own risk. A suitable generic battery would be a twelve volt, seven to nine amp-hour model.

If your UPS does turn out to be broken, I think APC still offers the "trade-UPS" program. This would provide a discount on a new unit and ensure the old one is properly recycled.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

0 Likes
0
2167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:49 AM . Last Modified: ‎2024-03-27 01:28 AM

thanks for the info William, very helpful!

I would clarify re the LEDs.  the green one does in fact remain on steady while the unit is in operation, and goes out when the unit fails.  I was meaning that the red LED does not come on, either steady or blinking red, when the unit fails.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of