Posted: 2021-06-29 07:41 AM . Last Modified: 2024-03-21 04:45 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM . Last Modified: 2024-03-21 04:45 AM
Is there a way to adjust to input voltage of BR1500i (220-240V) Back-ups? Because we're having problem when the input voltage goes low for about 215V-217V then our PC goes ON & OFF and UPS indicator shows "online" then "on-battery" blinking led. I'm wondering if it is possible to set the input voltage at around 180-200V?
Your immediate response is highly appreciated.
Regards,
Irwin
Electronics
Saipem
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM . Last Modified: 2024-03-21 04:45 AM
Good day thorz,
You can adjust the acceptable input voltage range of this unit manually by following these instructions:
!http://www.apc-forums.com/servlet/JiveServlet/download/21-7791-35334-2197/$710D2F297D5AA717.jpg!
Here's also a video of how to adjust the sensitivity manually.
Link: [http://nam-en.apc.com/app/answers/detail/a_id/10870]
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM . Last Modified: 2024-03-21 04:45 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM . Last Modified: 2024-03-21 04:45 AM
Please someone help me..
Thanks,
irwin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM . Last Modified: 2024-03-21 04:45 AM
Good day thorz,
You can adjust the acceptable input voltage range of this unit manually by following these instructions:
!http://www.apc-forums.com/servlet/JiveServlet/download/21-7791-35334-2197/$710D2F297D5AA717.jpg!
Here's also a video of how to adjust the sensitivity manually.
Link: [http://nam-en.apc.com/app/answers/detail/a_id/10870]
Link copied. Please paste this link to share this article on your social media post.