Posted: 2021-06-29 07:41 AM
This was originally posted on APC forums on 1/13/2012
Is there a way to adjust to input voltage of BR1500i (220-240V) Back-ups? Because we're having problem when the input voltage goes low for about 215V-217V then our PC goes ON & OFF and UPS indicator shows "online" then "on-battery" blinking led. I'm wondering if it is possible to set the input voltage at around 180-200V?
Your immediate response is highly appreciated.
Regards,
Irwin
Electronics
Saipem
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM
This reply was originally posted by Bernard on APC forums on 1/16/2012
Good day thorz,
You can adjust the acceptable input voltage range of this unit manually by following these instructions:
!http://www.apc-forums.com/servlet/JiveServlet/download/21-7791-35334-2197/$710D2F297D5AA717.jpg!
Here's also a video of how to adjust the sensitivity manually.
Link: [http://nam-en.apc.com/app/answers/detail/a_id/10870]
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM
This was originally posted on APC forums on 1/16/2012
Please someone help me..
Thanks,
irwin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:41 AM
This reply was originally posted by Bernard on APC forums on 1/16/2012
Good day thorz,
You can adjust the acceptable input voltage range of this unit manually by following these instructions:
!http://www.apc-forums.com/servlet/JiveServlet/download/21-7791-35334-2197/$710D2F297D5AA717.jpg!
Here's also a video of how to adjust the sensitivity manually.
Link: [http://nam-en.apc.com/app/answers/detail/a_id/10870]