Is it impossible to accurately measure the health of a Lead-Acid UPS?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is it impossible to accurately measure the health of a Lead-Acid UPS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
108
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

0 Likes
2
617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

Is it impossible to accurately measure the health of a Lead-Acid UPS?

In a blog post from Schneider Electric (parent company of APC), they say that lead-acid UPS batteries "rely on chemistry that makes it hard to accurately predict when they’re going to fail" but "Li-ion batteries always come with sophisticated battery monitoring systems (BMS) that provide a clear picture of battery runtime and health."

I haven't seen this documented anywhere else, although I have experienced unexpected UPS failure many times myself - even with UPS models that have a "replace battery" indicator. Having had too many UPS backups fail without warning, I am looking for a reliable UPS: either a lead-acid UPS with a battery meter (not just an indicator LED), or a UPS with a lithium-ion battery.

Can someone provide me with more information about the reliability of lead-acid batteries?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

0 Likes
0
617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

An important consideration is that most lithium battery systems use individual cell battery management, whereas lead/acid batteries very rarely use any individual cell monitoring at all (most designs prohibit effective monitoring).  One exception is the use of FLA (flooded) lead acid batteries with monitoring of individual cell specific gravities of the sulfuric acid.  This is tedious and generally only used by serious off-gridders, or industrial users - most auto batteries are designed to not access the electrolyte.  The UPS AGM batteries have no means to monitor individual cells, to do so would add unacceptable costs (they are very cheap in cost and construction!).  The maturing electric vehicle industry is the "master" of manufacturing, monitoring, managing, and protecting large number of lithium battery cells in series - any one of which can take down the entire battery!  IMO, the lithium battery industry will continually get better at this.  Imagine the next gen of EVs with 800 volt DC batteries - that is approx 200 "cells" in series.  That is going to require some serious "management".

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

0 Likes
0
617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

The BG500 (500VA, 300W) is lithium ion.

You'll note that the next level up, the BG700G (700VA, 420W) uses lead-acid and is cheaper though lacks network manageability. Since the battery lasts 3-5 years in a UPS environment, those who need reliability swap 'em out after three. The latest SmartUPS' automate this approach and proactively warn that the battery should be swapped out even if it hasn't failed (see this post).

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:09 AM . Last Modified: ‎2024-03-26 10:43 PM

An important consideration is that most lithium battery systems use individual cell battery management, whereas lead/acid batteries very rarely use any individual cell monitoring at all (most designs prohibit effective monitoring).  One exception is the use of FLA (flooded) lead acid batteries with monitoring of individual cell specific gravities of the sulfuric acid.  This is tedious and generally only used by serious off-gridders, or industrial users - most auto batteries are designed to not access the electrolyte.  The UPS AGM batteries have no means to monitor individual cells, to do so would add unacceptable costs (they are very cheap in cost and construction!).  The maturing electric vehicle industry is the "master" of manufacturing, monitoring, managing, and protecting large number of lithium battery cells in series - any one of which can take down the entire battery!  IMO, the lithium battery industry will continually get better at this.  Imagine the next gen of EVs with 800 volt DC batteries - that is approx 200 "cells" in series.  That is going to require some serious "management".

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore