Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Is SHARE-UPS compatible with SUM3000RMXLI2U?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is SHARE-UPS compatible with SUM3000RMXLI2U?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
3
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

Is SHARE-UPS compatible with SUM3000RMXLI2U?

Hi all,

I'm looking for a solution for multiple server shutdown with one Smart UPS.

I have 5 PC running on Windows 7, and want to shutdown them gracefully in case UPS is running on battery mode.

The initial configuration in my mind is:

1x     SHARE-UPS(AP9207)

1x     SUM3000RMXLI2U

5x     Smart Signaling (940-0024)

5x     Serial-to-USB converter

And each signaling connection would be SUM3000RMXLI2U --serial-- SHARE-UPS --serial(940-0024)-- --(serial-to-USB)-- Windows 7 PC.

With some googling, only smart signaling cable(940-0024) will work with serial-to-USB conversion.

The reason why I try the conversion is there are no serial ports on Windows 7 PCs.

Any comment will be appreciated.

HJ

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • share-ups
  • sum3000
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
0
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

So do those other servers have PowerChute Business Edition rpm on them? PowerChute Business Edition is what will be required for Share UPS. You'd install it in simple signaling mode on each Share UPS client.

And yes, most of the ports (there is one "Advanced port" for Smart Signaling) on the Share UPS will provide simple signaling which provides voltage on certain pins on the DB-9 port to indicate certain conditions one way from UPS->clients. Those conditions are UPS on battery, UPS low battery, and UPS turn off. I think the Share UPS might have some dip switch settings to customize when those signals occur.

I also am not sure on this UPS if you could use the management card and powerchute network shutdown AND an attached share UPS since the management card and the serial port are on the same communications bus. So you should do management card and powerchute OR share ups with powerchute business edition.

Lastly, I am not sure if its an option to execute a command files or a script from the clients that do support powerchute to shutdown the clients that do not (to avoid a share ups) or to use dry contact signaling from the AP9631.

Let me know if you have any other questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
0
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

Yes, Share UPS can work with that UPS.

A cheaper, easier solution would be to use the bundled AP9631 network management card included with that UPS model and install PowerChute Network Shutdown on each one of your  Windows 7 computers. As long as these Windows 7 computers are already on the network, you don't need all of those extra serial cables, Share UPS, etc.

So, you'd program the AP9631 with TCP/IP settings, install PowerChute Network Shutdown on your Windows 7 computers, and upon installing it, it will request the IP address of your AP9631 in your UPS. The Windows 7 computers and AP9631 in the UPS will keep constant communication over the network and provide a graceful shutdown option over the network as well. When the UPS is ready to shutdown in the manner you specify, it will signal the PowerChute clients over the network and they will shutdown.

This will also most likely workout a lot cheaper, require less cabling, and then you also have all of the nice features and capability of the pre-installed UPS Network Management Card (AP9631).

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
0
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

Hi Angela,

Thanks for the information. Actually, the servers are not all Windows 7 machines. Some are Linux based servers, and PowerChute compatible rpm package already installed on the servers - SM5000/NSM5200 from Pelco by Schneider Electric.

Those Linux servers doesn't allow network shutdown. That's the reason why I've come up with SHARE-UPS.

The other question: some other people are saying SHARE-UPS only replicates simple signal (like dry contact) and retransmit those to the rest of the ports. This means the simple signal would not go through serial-to-USB converter... finally it would not be a complete working solution.

Any comment on this?

HJ

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

0 Likes
0
1863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:57 PM . Last Modified: ‎2024-03-21 01:22 AM

So do those other servers have PowerChute Business Edition rpm on them? PowerChute Business Edition is what will be required for Share UPS. You'd install it in simple signaling mode on each Share UPS client.

And yes, most of the ports (there is one "Advanced port" for Smart Signaling) on the Share UPS will provide simple signaling which provides voltage on certain pins on the DB-9 port to indicate certain conditions one way from UPS->clients. Those conditions are UPS on battery, UPS low battery, and UPS turn off. I think the Share UPS might have some dip switch settings to customize when those signals occur.

I also am not sure on this UPS if you could use the management card and powerchute network shutdown AND an attached share UPS since the management card and the serial port are on the same communications bus. So you should do management card and powerchute OR share ups with powerchute business edition.

Lastly, I am not sure if its an option to execute a command files or a script from the clients that do support powerchute to shutdown the clients that do not (to avoid a share ups) or to use dry contact signaling from the AP9631.

Let me know if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore