Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Is SHARE-UPS compatible with SUM3000RMXLI2U?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Is SHARE-UPS compatible with SUM3000RMXLI2U?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:57 PM

0 Likes
3
180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:57 PM

Is SHARE-UPS compatible with SUM3000RMXLI2U?

This question was originally posted by Hyung-Je on APC forums on 3/17/2013


Hi all,

I'm looking for a solution for multiple server shutdown with one Smart UPS.

I have 5 PC running on Windows 7, and want to shutdown them gracefully in case UPS is running on battery mode.

The initial configuration in my mind is:

1x     SHARE-UPS(AP9207)

1x     SUM3000RMXLI2U

5x     Smart Signaling (940-0024)

5x     Serial-to-USB converter

And each signaling connection would be SUM3000RMXLI2U --serial-- SHARE-UPS --serial(940-0024)-- --(serial-to-USB)-- Windows 7 PC.

With some googling, only smart signaling cable(940-0024) will work with serial-to-USB conversion.

The reason why I try the conversion is there are no serial ports on Windows 7 PCs.

Any comment will be appreciated.

HJ

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • share-ups
  • sum3000
  • usb
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:57 PM

0 Likes
0
180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:57 PM

This reply was originally posted by Angela on APC forums on 3/19/2013


So do those other servers have PowerChute Business Edition rpm on them? PowerChute Business Edition is what will be required for Share UPS. You'd install it in simple signaling mode on each Share UPS client.

And yes, most of the ports (there is one "Advanced port" for Smart Signaling) on the Share UPS will provide simple signaling which provides voltage on certain pins on the DB-9 port to indicate certain conditions one way from UPS->clients. Those conditions are UPS on battery, UPS low battery, and UPS turn off. I think the Share UPS might have some dip switch settings to customize when those signals occur.

I also am not sure on this UPS if you could use the management card and powerchute network shutdown AND an attached share UPS since the management card and the serial port are on the same communications bus. So you should do management card and powerchute OR share ups with powerchute business edition.

Lastly, I am not sure if its an option to execute a command files or a script from the clients that do support powerchute to shutdown the clients that do not (to avoid a share ups) or to use dry contact signaling from the AP9631.

Let me know if you have any other questions.

See Answer In Context

Reply
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:57 PM

0 Likes
0
180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:57 PM

This reply was originally posted by Angela on APC forums on 3/18/2013


Yes, Share UPS can work with that UPS.

A cheaper, easier solution would be to use the bundled AP9631 network management card included with that UPS model and install PowerChute Network Shutdown on each one of your  Windows 7 computers. As long as these Windows 7 computers are already on the network, you don't need all of those extra serial cables, Share UPS, etc.

So, you'd program the AP9631 with TCP/IP settings, install PowerChute Network Shutdown on your Windows 7 computers, and upon installing it, it will request the IP address of your AP9631 in your UPS. The Windows 7 computers and AP9631 in the UPS will keep constant communication over the network and provide a graceful shutdown option over the network as well. When the UPS is ready to shutdown in the manner you specify, it will signal the PowerChute clients over the network and they will shutdown.

This will also most likely workout a lot cheaper, require less cabling, and then you also have all of the nice features and capability of the pre-installed UPS Network Management Card (AP9631).

Hope that helps.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:57 PM

0 Likes
0
180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:57 PM

This reply was originally posted by Hyung-Je on APC forums on 3/19/2013


Hi Angela,

Thanks for the information. Actually, the servers are not all Windows 7 machines. Some are Linux based servers, and PowerChute compatible rpm package already installed on the servers - SM5000/NSM5200 from Pelco by Schneider Electric.

Those Linux servers doesn't allow network shutdown. That's the reason why I've come up with SHARE-UPS.

The other question: some other people are saying SHARE-UPS only replicates simple signal (like dry contact) and retransmit those to the rest of the ports. This means the simple signal would not go through serial-to-USB converter... finally it would not be a complete working solution.

Any comment on this?

HJ

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:57 PM

0 Likes
0
181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 07:57 PM

This reply was originally posted by Angela on APC forums on 3/19/2013


So do those other servers have PowerChute Business Edition rpm on them? PowerChute Business Edition is what will be required for Share UPS. You'd install it in simple signaling mode on each Share UPS client.

And yes, most of the ports (there is one "Advanced port" for Smart Signaling) on the Share UPS will provide simple signaling which provides voltage on certain pins on the DB-9 port to indicate certain conditions one way from UPS->clients. Those conditions are UPS on battery, UPS low battery, and UPS turn off. I think the Share UPS might have some dip switch settings to customize when those signals occur.

I also am not sure on this UPS if you could use the management card and powerchute network shutdown AND an attached share UPS since the management card and the serial port are on the same communications bus. So you should do management card and powerchute OR share ups with powerchute business edition.

Lastly, I am not sure if its an option to execute a command files or a script from the clients that do support powerchute to shutdown the clients that do not (to avoid a share ups) or to use dry contact signaling from the AP9631.

Let me know if you have any other questions.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc