Faulty battery can cause the breaker to trip?
Showing results forΒ
Did you mean:Β
  • Faulty battery can cause the breaker to trip?
2151
123
Posted: β€Ž2021-06-29 07:57 PM . Last Modified: β€Ž2024-03-21 01:23 AM
5416
Hi All
If the battery is faulty it can cause the breaker to trip?
Our remote office have 1 APC UPS Su3000RMXLI the unit was totaly down, i try to power up the unit but the breaker was trip. I try to open the battery module then i found that the some of the battery bloated already. Our vendor replace the faulty battery module and the unit is working fine.
So my question is why the breaker trip? If the battery is the cause can you help to to explaine coz i really can't understand why.,Thanks in advance
  • Universal Transfer Switch
Posted: β€Ž2021-06-29 07:57 PM . Last Modified: β€Ž2024-03-21 01:22 AM
it just once, rigth now the UPS is working fine, but yeah just a curios why the ups trip the breaker...,E
Replies 8
hmm, at first glance, this does not seem likely.
on the back of this particular UPS, i believe there is an input circuit breaker, which is near the input power connection and then there may be output circuit breakers. from the pictures i can see, it only looks like the output breakers are on the 120v models but can you confirm?
it is a 40 amp breaker so for that to trip, the UPS needed to draw more than 40 amps (overload) or something shorted it out to believe it did. what is the load on this particular UPS - the percentage (or how many load LEDs on the front left of the display panel are lit up) as well as the type of equipment?
you said it was a remote office - so was there nobody there that could have possibly hit the breaker accidentally or anything like that?
did you have any software/network management card or anything monitoring the UPS?
Hi
FYI, the ups input voltage 220-240Vac, and there is no circuit breaker at the output side, the input breaker didn't trip, only the main circuit breaker ( utility breaker ) was trip, coz we install a circuit breaker at the input supply of the ups, yah nobody on the site and im the only one who have a key for the network room,.
The equipment connected to he ups is only 5 cisco switches, no load LED lights up and no NMC card was installed in out unit.
Hi All
Any one can give me a idea, regarding this issue? thanks in advance
what size is the upstream utility breaker?
sorry for the reply take so long, the utility breaker is 30A and the UPS side input current 16A was indicated/ printed at the back of the unit. Im so curios why if the battery is faulty and we try to switch on then the breaker will trip. Thanks
something must have shorted it out i am assuming. is it still doing it or it only did it once?
yeah i am not sure based on the information you were able to give πŸ˜•
Β