How to know when UPS and/or battery needs replaced?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • How to know when UPS and/or battery needs replaced?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

0 Likes
5
6927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

How to know when UPS and/or battery needs replaced?

I have the APC CS 500 (BK500BLK) UPS unit and the other day all components connected to this unit lost power. I did not lose power in the house and did not hear the UPS unit beep for any reason. When I looked at the UPS unit, the green "On-Line" light was on, but none of the components had power. I turned the unit off and then back on and the components regained their power.

The unit is probably 5 years and I have never replaced the battery and the "Replace Battery" light has never come on.

Is this an indication that the unit itself is bad and/or that the battery should be replaced even though the "Replace Battery" light has never come on?

Thanks.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
0
6927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

You are welcome Brian!

Secondly, you may have a look at the K-base[titled Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=20].

Please let us know if you have any question.

Have a nice day!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

0 Likes
0
6927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

Brian,

APC Back UPS CS UPS is designed to perform a self test at start up and every 14 days to check the battery integrity. Typical battery life is three to five years depending on use and environment (temperature). Secondly, the battery normally lose its ability to hold a charge if it is more than three to five years. In order to find if the issue you mentioned lies with the battery or the unit, I would like to gather some more information from you. What are the equipment you have attached to the battery backup outlets? Do you have PCPE software installed on your Computer to manage the UPS? If so, what is the UPS runtime showing on Software? If possible, could you please perform the Self test and check if the unit passes the Self test?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

0 Likes
0
6927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

Techie...thanks for your response !

I have the following components connected to the UPS:

Battery backup ports:

  • Netgear GS108 8-port Switch

  • DELL E173FPc 17" LCD Monitor

  • ReadyNAS NV

Surge only ports:
  • ReadyNAS PRO

  • Dell Dimension 3000

  • Dell Dimension 3000


In performing the self-test, I turned the unit off and waited several seconds and turned it back on. The "On-Line" light flashed for a couple seconds and then the "On-Battery" light flashed for a couple seconds, then the "On-Line" flashed again and stayed on. I do not have the PCPE software installed on a computer for I have the ReadyNAS attached to the APC data port.

Thanks again for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

0 Likes
0
6927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

Brian,

Thank you for the information. Had the UPS been providing adequate runtime during power failure before? It looks like that the battery in the unit needs to be replaced. Do you have other Identical working unit with good known battery? If so, swap the batteries and check if the unit in question supports the load. This will help us to determine if the issue lies with the battery or the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

0 Likes
0
6926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:03 AM

The unit seemed to be fine previous to the other day. The curious thing is I haven't had a power outage in months yet the components attached to the UPS were all powered off while the "On-Line" light was on.

I don't have a spare battery to swap in, so I guess I'll keep monitoring the UPS and see if I have any other issues.

Thanks so much for your time.

It appears that I should be able to award you points, however I don't see that option when I post?

Sorry, I now see I should have checked "Mark this thread as a question" with my first post in order to award you points.

Message was edited by: needupshelp

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
0
6928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

You are welcome Brian!

Secondly, you may have a look at the K-base[titled Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=20].

Please let us know if you have any question.

Have a nice day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore