Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How the die battery affect UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • How the die battery affect UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
StevenX
StevenX
Explorer

Posted: ‎2025-10-08 02:15 PM

0 Likes
4
2389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-08 02:15 PM

How the die battery affect UPS

1. We have a SMX3000LVNC which is connecting 4 external SMX120BP which was bought 11 years ago, we temporarily name these four external pack as Bat1, Bat2, Bat3 and Bat4. If battery in Bat2 dies, how many battery pack will continue support UPS? Only Bat1 or Bat1 plus Bat3 and Bat4?

2. We want to buy new batteries to replace the old battery in SMX120BP. 

What's the new battery model compatible with SMX120BP and SMX3000LVNC?

How can I replace batter safety and while replacement, do I need to power off SMX3000LVNC? 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2025-10-10 05:53 AM

In response to StevenX
0 Likes
0
2368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-10 05:53 AM

You may refer to this CSB Resource Link for the individual cells inside of the RBC:

 

https://csb-battery.ca/products/hr1221wf2


As stated what happens depends upon what state (condition) the individual cells within the RBC (Replacement Battery Cartridge) are in.

 

In the extreme case where the RBC is completely dead if there is an outage and requires the system to transfer to battery only power.

 

The system will drop the attached loads and shutdown. In a best case scenario depending upon actual load you’ll see a few minutes (1-5) of operational runtime vs the expected of whatever say 30-60 minutes.

 

Any serious enterprise installation will perform daily, monthly, yearly maintenance and inspections of the power delivery management systems.

 

This spans from very basic visual inspection of the LCD parameters, UPS frame, input / output wiring / identification, connected loads, and logs.

 

To battery production & installations date, RBC inspection of cartridges, etc.

 

Annual Static & Dynamic load testing is conducted to validate the entire system is fully operational and ready to perform when needed. This also encompasses validating all cells within the RBC are still within the battery manufacturers internal resistance values so the expected minimum operational runtime is obtained during a lights out / grid down event.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Teken
Teken
Champion

Posted: ‎2025-10-09 01:42 AM

0 Likes
1
2386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-09 01:42 AM

How the system behaves depends upon many factors such as if all RBC are the same health, installation date, and capacity.

 

If all RBC are truly 11 years old that is absolutely ridiculous and someone needs to be fired! 🤦‍♂️

 

The RBC is rated to provide 2-5 years of service life based on usage, temperature, and environmental conditions. They are designed to sustain 260 cycles before degradation is seen.

 

The best case scenario is you will see shorter operational runtime. Worst case the bad cells in each RBC will drag down other RBC and cause the system to shutdown. 

In the extreme cases the RBC will bulge, over heat, vent, and cause an explosive situation if there is a electrical spark.

 

Im not sure what you mean by newer battery model?!? The APC OEM is RBC143 so if the question is about rebuilding the RBC then you can simply purchase ten of the same CSB 12 VDC 5 AH cells and rebuild it which is much cheaper than buying two RBC cartridges.

 

Lastly, the SMX is hot swappable as such you do not need to power down the system. The only caveat is (IF) the RBC’s are dead during a power outage / disruption the system will obviously shutdown as the RBC can’t sustain the connected loads.

 

So either replace the RBC pairs from top down in sequence or rebuild the RBC and replace them the same way as outlined above.

 

Once all RBC have been replaced update the battery installation date in the system. Mark the same on every RBC cartridge on the face.

 

Manually initiate a self test and let pass and allow the system to return to 100% SOC (State of Charge).

 

Complete the process by manually initiating a battery calibration with at least 30% or greater attached load. Once completed allow the system to fully charge the entire battery pack / system.

 

The operational runtime will be more accurately displayed via LCD, NMC, SNMP

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenX
StevenX
Explorer

Posted: ‎2025-10-09 04:12 PM

In response to Teken
0 Likes
0
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-09 04:12 PM

Hello Teken, I googled CSB 12 VDC 5 AH cell, and got many battery models. Which battery model is APC filling into SMX120BP? 

Reply

Link copied. Please paste this link to share this article on your social media post.

StevenX
StevenX
Explorer

Posted: ‎2025-10-09 04:24 PM

0 Likes
1
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-09 04:24 PM

As my understand, multiple SMX120BP is connected in parallel, inside cells are connected in serial so if one cell dies, it will make the host SMX120BP stop working, so that master smart UPS like our SMX3000LVNC will lost some battery running time, not all SMX120BP support. Am I correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-10-10 05:53 AM

In response to StevenX
0 Likes
0
2369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-10 05:53 AM

You may refer to this CSB Resource Link for the individual cells inside of the RBC:

 

https://csb-battery.ca/products/hr1221wf2


As stated what happens depends upon what state (condition) the individual cells within the RBC (Replacement Battery Cartridge) are in.

 

In the extreme case where the RBC is completely dead if there is an outage and requires the system to transfer to battery only power.

 

The system will drop the attached loads and shutdown. In a best case scenario depending upon actual load you’ll see a few minutes (1-5) of operational runtime vs the expected of whatever say 30-60 minutes.

 

Any serious enterprise installation will perform daily, monthly, yearly maintenance and inspections of the power delivery management systems.

 

This spans from very basic visual inspection of the LCD parameters, UPS frame, input / output wiring / identification, connected loads, and logs.

 

To battery production & installations date, RBC inspection of cartridges, etc.

 

Annual Static & Dynamic load testing is conducted to validate the entire system is fully operational and ready to perform when needed. This also encompasses validating all cells within the RBC are still within the battery manufacturers internal resistance values so the expected minimum operational runtime is obtained during a lights out / grid down event.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore