Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How big of a UPS can I use for the UTS10BI?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • How big of a UPS can I use for the UTS10BI?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
5
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

How big of a UPS can I use for the UTS10BI?

I wish to maximize the 1800W limit on the UPS inlet for the UTS10BI.  If I used an APC SMT220 would I be okay?  I know that its rated output is 1920W, but if I move down to another model then I can't utilize the full 1800W capability on the UTS10BI input.  Comments and suggestions are appreciated.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:07 PM . Last Modified: ‎2024-03-20 12:53 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:07 PM . Last Modified: ‎2024-03-20 12:53 AM

Angela N.

Thank you, I love your explanations, they make sense.

Nelson

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:53 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:53 AM

I wish to maximize the 1800W limit on the UPS inlet for the UTS10BI.  If I used an APC SMT220 would I be okay?  I know that its rated output is 1920W, but if I move down to another model then I can't utilize the full 1800W capability on the UTS10BI input.  Comments and suggestions are appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:53 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:53 AM

hello. i think there is a little mistake here on the UTS's part unfortunately.

the convenience outlet on the UTS10BI for the optional UPS is 5-15R. the plug on an SMT2200 is a 5-20P and will not fit into a 5-15R receptacle. the 1800 watts is also a little misleading. 5-15R indicates an 120V receptacle rated at 15 amps. 5-20R is a 120V 20 amp receptacle. if we take 1800 watts and divide it by 120V, that gives us 15 amps. basically, i think someone made a mistake here with the calculation for the wattage in the UTS because a 5-15R is 15 amp receptacle but national electrical code here in the UPS de-rates it by 20% to 12 amps (that de-rating rule is outlined in article FA157467 in our knowledge base @ www.apc.com/site/support/index.cfm/faq/ ). thus, to get the max wattage this receptacle could provide, we should do 12A multiplied by 120V which gives us 1440 watts. then you also need to worry about power factor when choosing a UPS because all of our UPSs that have a 5-15P will max out at 1440 volt amps (VA) but their actual power output in watts is a little less due to the power factor of the UPS. power factor is the ratio of volt amps (apparent power) to actual power (watts).

hope i haven't confused you but technically, you cannot use a UPS with more than 1440W output with 5-15R that is on the front of the UTS because if you even changed the plug on your SMT2200 to plug it in, you're effectively wasting part of the UPS power output. changing the plug de-rates it to the 1440VA. If our UPSs had a power factor of one, then the VA rating would match the watts rating but none of the Smart UPS have that. There is some info on de-rating when you change a plug listed in article FA156517 in the knowledge base too.

essentially, to get the max you possibly could (1440W), look at something with a 1500VA rating and check the wattage rating of it as well. the ratio between that VA rating and watt rating you see listed on our web pages is that power factor ratio and essentially is what is lost through heat dissipation and in UPS operation. if you or any of the other readers want more information on power factor and watts vs. VA), article FA157485 covers that.

I suggest BR1500G, BX1500G, SMT1500, SMX1500, etc depending on what features you want in a UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:53 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:53 AM

Thank you very much and, no, the answer does not confuse me.  It all makes sense now.  I really appreciate the detailed answer and I certainly love the product.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 11:07 PM . Last Modified: ‎2024-03-20 12:53 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:07 PM . Last Modified: ‎2024-03-20 12:53 AM

Hi Nelson,

1. Yes - because of the receptacle type on the UTS. It is a 15A receptacle but per National Electrical Code, a circuit must be de-rated to 80% of its capacity. The 1800 watts assumes 100%.

2. The numbers in the model numbers of most UPSs indicate the VA or Volt Amps. Because of efficiency and power factor on the UPS itself (which most UPS models, especially smaller ones, do not have a unity power factor), you'll see a difference in how many volt amps versus watts a UPS could provide. The way to size a UPS would be watts since that is your "real power" versus volt amps which is "apparent power."

3. If you can find a UPS that has a 15A plug (de-rated to 12A per NEC) and outputs 1440, yes, you could use it. The UPSs around this size we offer would either be Back UPS or Smart UPS and we'd have to see which one offers the best rating. The smaller the difference between watts and VA, the more expensive it will likely be. A value type Smart UPS (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SMC1500) does 900 watts if you take a peek. We also have either SMX1500 types or SMT1500 types but SMC1500 is cheaper and doesn't have as many bells and whistles as those Smart UPS.

4. Refer to #3 smile

Hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:07 PM . Last Modified: ‎2024-03-20 12:53 AM

0 Likes
0
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:07 PM . Last Modified: ‎2024-03-20 12:53 AM

Angela N.

Thank you, I love your explanations, they make sense.

Nelson

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore