Highest Possible VA from a 15amp UPS?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Highest Possible VA from a 15amp UPS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
5
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

Highest Possible VA from a 15amp UPS?

I think I posted this in the wrong section earlier...

Can anyone tell me what the highest VA is that I can get from a 15amp UPS?

Also I've got a APC UPS Model# DLA1500, was just wondering where I could get a replacement battery for this for cheap?

Thanks,
G

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • assembly
  • battery
  • rbc7
  • smartups_1400
  • third_party
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:51 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
0
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:51 PM . Last Modified: ‎2024-03-21 03:23 AM

Here's an article I wrote some time ago on how to assemble bare batteries into one of the most common APC RBC, APC RBC7 compatible pack.
http://www.wikihow.com/Assemble-an-APC-Rbc7-Smart-Ups-Battery

In place of Plastic Weld, I tried Gorilla glue and it too works very good, however you need to lay the batteries on the side and secure the two halves with tapes so they don't slide around while the glue is curing.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
0
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

The SUM units have the highest output rating in terms of watts.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUM1500RMXL2U

The DLA1500 uses an RBC7.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
0
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

Other spec pages that I saw for different UPS units had a specification saying they were 15 amps, where can I find out how many amps these ones are (The one you mentioned above and others like it)?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
0
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

A UPS is rated (per electrical code) for 80% of its plug type. So, that UPS that was posted by EZ Button, the SUM1500RMXL2U, has a 15 amp plug (the 5-15 indicates 15 amps - 5-20 would be 20 amps) on it so it is rated for 12 amps for the output. (80% of 15 amps)
Thus, a UPS with a 20 amp plug is rated for 16 amps.

Hope that answers your question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
0
2639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:50 PM . Last Modified: ‎2024-03-21 03:23 AM

GagguP wrote:
I think I posted this in the wrong section earlier...

Can anyone tell me what the highest VA is that I can get from a 15amp UPS?

Also I've got a APC UPS Model# DLA1500, was just wondering where I could get a replacement battery for this for cheap?

Thanks,
G
15A circuit allows 12A continuous, so the maximum permissible is 120 x 12 = 1440VA.
The DLA 1500 is 1440VA/980W which assumes 0.7 power factor. With the introduction of 80Plus program and environmental awareness, many computers today have a power factor exceeding 0.95.

So, the permissible load is 1440VA or 980W, whichever is lower, depending on load power factor. If you have servers with PFC, you will only get about 1000VA/980W.

I always get replacement batteries from Gruber Power Services in Arizona through eBay. You can find their stuff through eBay or call them at
800-658-5883

Although if you're buying one or two sets, buying from them on eBay is the best way. I'm sure you can find others with similar deal, although be aware of dealers with old stock.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:51 PM . Last Modified: ‎2024-03-21 03:23 AM

0 Likes
0
2640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:51 PM . Last Modified: ‎2024-03-21 03:23 AM

Here's an article I wrote some time ago on how to assemble bare batteries into one of the most common APC RBC, APC RBC7 compatible pack.
http://www.wikihow.com/Assemble-an-APC-Rbc7-Smart-Ups-Battery

In place of Plastic Weld, I tried Gorilla glue and it too works very good, however you need to lay the batteries on the side and secure the two halves with tapes so they don't slide around while the glue is curing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore