Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84505members
353719posts

HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
87

HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

This question was originally posted by Franklin on APC forums on 9/10/2010


HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
87

HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

This reply was originally posted by Franklin on APC forums on 9/11/2010


HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
87

Re: HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

This reply was originally posted by Matt on APC forums on 9/15/2010


So once all the modules were installed, and system enable turned ON. The UPS showed only the green Load ON and orange Bypass LEDs on the PowerView display?

Then when you turn off the maintenance bypass switch, the UPS goes online successfully, showing only the Load-On LED on the PowerView, but your equipment reboots?

As mentioned previously, there is a slight break transfer when the UPS is transitioning online from bypass 4-6 milli-seconds. Almost all equipment has no issue with this transfer time, but you may have equipment with older power supplies which cannot sustain operation during the transfer-time.

If there are faults/alarms or RED LED on the PowerView display, please share that information.

BillP
Administrator Administrator
Administrator
0 Likes
0
87

Re: HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

This reply was originally posted by Franklin on APC forums on 9/14/2010


Hi Joe:

Yes. the UPS was on manual bypass, with built-in maintenance bypass switch, located to the right of the PowerView display, and the input breaker was engaged and System Enable switch off. Then, we pull out and cleaning the power modules and tried to back on line. We inserted againg the power modules, and turn on the system enable switch. The UPS display show "UPS in Bypass", but when disengaging the LX maintenance bypass switch (located to the right of the PowerView) to force UPS OnLine the load (servers) turn off and restared.

Thanks,
Frank

BillP
Administrator Administrator
Administrator
0 Likes
0
88

HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD

This reply was originally posted by Franklin on APC forums on 9/11/2010


HOW TRANSFER SYM LX FROM MANUAL BYPASS TO ONLINE WITHOUT DROP THE LOAD