Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

H15 a good choice, even though......?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: H15 a good choice, even though......?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
154
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:54 AM

0 Likes
7
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:54 AM

H15 a good choice, even though......?

Hi all,

My monster power HTS 2500mkII kicked the bucket recently and I am in need of a new unit. I will not be returning to Monster Power this time. I was about to push the button on a panamax unit, when I came across the APC series of AV protectors. The H15 is appealing to me BUT......I have 2 rather large amplifiers (an Aragon 4004mkII and a Hafler XL-600) I have heard of people having issues with the voltage regulation when using certain power amplifiers. I don't think the rest of my gear would present any problems, but the amps worry me. I don't want THEM damaged, and don't want to damage the APC, either.

Anyone have any experience with this? Would I be better off with a different model?

Thanks for any information/responses!

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: β€Ž2021-06-29 07:31 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:31 PM . Last Modified: β€Ž2024-03-21 02:53 AM

you can post on this thread as much as you like πŸ˜›

the AVR should only be active while the voltage is low. so if the amps go back to normal, the voltage should jump back up on the line and the AVR will go off. basically, the unit should never provide excessive voltage to the connected equipment regardless of what happens.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

"Let's say the amplifiers turn on, and one or both fools the H10/H15 into thinking it's a voltage sag....causing the AVR to kick in and raise the voltage...in the meantime the amps have returned to normal...could the excess voltage the H10/15 puts out potentially harm the amps or other equipment, which are now getting more voltage than they need?"

I have the same concern as Tull1996. I have been using the H10 for about a year. I often see the AVR kicks in while my DENON receiver is turning on, and then the AVR goes off as soon as the receiver is on. I thought it happens because the DENON demands too much current, and the AVR just does it job to supply more current. However, recently, the power outlets in my living room have complettly broken. It makes me to really wonder whether or not the damage was caused by the H15 or the electrical circuit in my house.
Any suggestion about what I can do to prevent the AVR to kick in while the receiver is turning on? I dont think it turns on because the voltage is low. Sometime, I turn on the receiver even while other appliances that are connected to the H15 are currently on and drawing currents, and the AVR feature would still not be activated.
Thank you very much.

Message was edited by: thientai

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

you can try to adjust the AVR range. the unit should not be boosting/trimming the voltage to unacceptable levels for the attached equipment. if the unit allowed that, certainly things would become damaged if they were supplied extra voltage.

are you able to see what the input/output voltage is when this happens?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

we'd have to check the specs on those amps but the inrush current problem would really be related to the thermal ratings of the breakers since this device, the H15, is a surge protector with AVR in general terms.

the only thing i can see happening is if the current is SO much that it causes a brownout/sag on the line, then the AVR may kick in but that is about it.

i dont see why this unit wouldnt be able to handle it. it also has delayed outlets so that everything doesnt turn on at the same time.

do you definitely just want AVR and surge protection or are you interested in a UPS as well? our AV UPSs, cause they have inverters, are very beefy and can handle in rushes up to 250% for a couple of seconds on certain models.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

Hi,

Thanks for the reply. I'm not sure what specs would be valuable to you concerning the amps, but the Aragon puts out 200wpc into 8ohms, and the Hafler puts out 305wpc into 8ohms. I know they are both considered high current amps but don't know the actual numbers. I DO know that the Hafler dims the lights momentarily when it first turns on....

As far as the UPS...although I love the idea, they are a little rich for my blood. I'm more concerned with whether I should get the H15 WITH the voltage regulator, or if I should get something like the C10 which (I believe) has the same surge and spike protection, but does not have the voltage regulation feature.

I will definitely be going with SOMETHING from APC....I have several computers at home all using a variety of APC UPS units, and as an IT Technician at a network affliliate television station, we use larger APC UPS units on all of our critical systems, and none have ever let me/us down.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

yeah i mean its all what you need. if you dont want a UPS, I think you will still see the lights dim when turning these pieces of equipment turning on even with some type of AV surge protector type of thing.

if you experience a lot of brownouts/sags/overvoltages, i'd go with the AVR. If not, i think a C type device should suit you just fine. you are right in saying that the C type has all the same surge protection as the H type besides the AVR. the H type also is a bigger box with some more indicators/LEDs on the front.

let me know if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:30 PM . Last Modified: β€Ž2024-03-21 02:53 AM

Well, as a last question and concern.....and maybe my thought process here is incorrect....

Let's say the amplifiers turn on, and one or both fools the H10/H15 into thinking it's a voltage sag....causing the AVR to kick in and raise the voltage...in the meantime the amps have returned to normal...could the excess voltage the H10/15 puts out potentially harm the amps or other equipment, which are now getting more voltage than they need?

I promise this will be the last question I make on this thread! πŸ˜‰

Thanks for your help so far!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: β€Ž2021-06-29 07:31 PM . Last Modified: β€Ž2024-03-21 02:53 AM

0 Likes
0
2034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 07:31 PM . Last Modified: β€Ž2024-03-21 02:53 AM

you can post on this thread as much as you like πŸ˜›

the AVR should only be active while the voltage is low. so if the amps go back to normal, the voltage should jump back up on the line and the AVR will go off. basically, the unit should never provide excessive voltage to the connected equipment regardless of what happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore