Get Power Consumption

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Get Power Consumption
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:09 AM

0 Likes
4
4303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:09 AM

Get Power Consumption

Hi

Is there a way to read out my connect equipments power usage, either with apcaccess or some other command?

I am running apcupsd, with usb cable, ubuntu 18.04 server. 
Power-Saving Back-UPS Pro 1500

VERSION : 3.14.14 (31 May 2016) debian
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2020-08-30 10:58:39 +0000
MODEL : Back-UPS RS 1500G

The only power reading I can find is NOMPOWER but that is not matching the ~200W I am expecting, it says 865W.

Are there other command that I can use to get the power usage?

BR,
Peter

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

0 Likes
0
4303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

Hi Bill,

thank you for your test results! Seem like my power meter and the UPS are giving the same results then. I have nothing connected to the surge only outlets. It's just a NAS and an esxi server and I wan't to have both on the battry/surge outlets of course. 🙂

I'll have to do some more follow up tests I think. I just go this new UPS a few days ago.

BR,
Peter

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

0 Likes
0
4303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

Hi,

The software does not give that data directly. However, if you pull LOADPCT and multiply NOMPOWER by LOADPCT you will get the draw wattage. Example: NOMPOWER reads 865, LOADPCT reads 20% so 865 times .20= 173 Watts.

NOTE: When pulling LOADPCT the UPS is only reporting what is being drawn from the Battery / Surge outlets. The number does not include what is being drawn from the Serge only outlets. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

0 Likes
0
4303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

Thanks for the reply!

I am not sure that is correct, that would in my case be 865W * 11% = 95W. I have a power meter connected to the socket to which only the UPS it is connected. That power meter has never been below 115W (currently 128W). Does the UPS itself draw 20-30W in addition to the equipment that I have connected to it?

BR,
Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

0 Likes
0
4303
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

Hi,

I have a BR1500MS. I plugged the UPS into a Kill A Watt meter and with no load, it reads 2 - 4 watts while not charging. After running on battery the meter read 16 – 18 watts and decreased over time until settling at 2 - 4 watts.  

With a 150 watt lamp connected the meter reads 152 - 154 watts when fully charged. When I plug the meter into the UPS, connect the load to the meter, the meter reads 148 watts. At that time, APCUPSD reports NOMPOWER 900 watts, LOADPCT 16%, 900 * .16 = 144. Slightly less than the Kill A Watt meter reading of 148.

Please remember, the UPS is only presenting the load on the battery/surge outlets to the software. It does not report the draw on the surge-only outlets. So, if you have something plugged into the surge-only outlets with the meter attached to the wall the software will report less load then the meter. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

0 Likes
0
4304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 PM . Last Modified: ‎2024-03-26 03:08 AM

Hi Bill,

thank you for your test results! Seem like my power meter and the UPS are giving the same results then. I have nothing connected to the surge only outlets. It's just a NAS and an esxi server and I wan't to have both on the battry/surge outlets of course. 🙂

I'll have to do some more follow up tests I think. I just go this new UPS a few days ago.

BR,
Peter

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore