APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-09 07:03 AM
Hello!
We have a Smart-UPS 3000 (SMT3000RMI2U) in use. Recently it has been reporting a critical alarm: “At least one faulty battery exists.”. I then unplugged the battery for 2 minutes and plugged it back in. After a manual self-test, the error disappeared and there was no more trouble. It should also be mentioned that the battery was replaced between 1 and 1.5 years ago.
After the next scheduled self-test, the error was there again.
My next step would now be to update the firmware. The firmware revision shown is UPS 09.3 (ID18). According to this (_ttps://www.se.com/de/de/download/document/Smart-UPS_FW_Release_Notes/), the correct and current update would be “SMT18UPS_15-0.enc”. In the corresponding PDF it says:
“Applicable Models:
==================
Smart-UPS SMT UPSs (except 1U) rated 0.75, 1 & 1.5 kVA with ID 18”
Our UPS states:
“Apparent Power Rating
3000 VA” ...i in other words 3kVA.
Is there another update? Or is there no suitable update for this (I can hardly believe it)? Or can I install it anyway?
The NMC (AP9631) HWrev08 is already at version v7.1.8 from September 2024.
Many thanks for your help and have a nice weekend.
Mr. T \m/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-09 09:12 AM
The average service life of the battery cartridge is 2-5 years. Based on usage, temperature, and environmental conditions.
Provide an image capture of the battery cartridge production sticker and the installation date from the NMC Configuration -> UPS tab.
The NMC will provide the serial number and production date of the UPS from the (About UPS) tab - provide it here.
Dynamic Test: Remove AC Mains from the system while under normal load and report back the results. There are only three possible outcomes during the lights out / grid down test.
Complete shutdown, limited operational runtime, acceptable operational runtime vs a new RBC.
Report back the results and outcome. A UPS Firmware upgrade is absolutely the last thing you need to even consider! ☝️
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-09 10:29 PM
Hello Teken!
Thank you very much for your answer. I will be on site next time on Sunday and will carry out the test and record and provide the requested information.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.