APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-01-08 09:41 AM
Hello,
I've had this UPS since 2019 and it's no longer in warranty. I've never actually tested that it works but the other day, I unplugged it from the wall, it switched to battery for half a sec and turned off even though the battery meter said 100% on both the LCD and in Powerchute.
I thought the battery was dead so I bought another one, put it in and left it charging for an entire day, same thing. Turns off almost immediately after unplugging. The battery meter continues to show 100% even if I disconnect the battery from the unit.
What can I do now?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-01-09 06:01 AM
Complete the following action items in this specific order and report back the results:
Brain Dead:
https://www.apc.com/us/en/faqs/FA158947/
Installation Date: Update the battery installation date via Power Chute.
Self Test: Manually initiate a self test and let it complete. If this step fails call this out with the error message.
Battery Calibration: Once the battery is 100% SOC (State of Charge). Initiate a battery calibration with at least 30% attached load on the outputs. Let this process complete and battery return to 100% SOC.
Wait an hour than remove AC Mains from the wall outlet. What are the results of doing so?!? Report back what Power Chute indicates as the current load (power) and estimated runtime while running on battery only mode.
Questions Ask . . . đź‘Ť
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-01-10 09:52 AM
Brain Dead: https://www.apc.com/us/en/faqs/FA158947/
Done - note that the battery indicator on the LCD and in Powerchute still shows 100% charged even if battery is disconnected.
Installation Date: Update the battery installation date via Power Chute.
Done
Self Test: Manually initiate a self test and let it complete. If this step fails call this out with the error message.
Passed
Battery Calibration: Once the battery is 100% SOC (State of Charge). Initiate a battery calibration with at least 30% attached load on the outputs. Let this process complete and battery return to 100% SOC.
No such option in Powerchute or the onscreen menu. Tried to manually calibrate by putting a 30% load and unplugging from wall, i hear a click and it turns off.
I've tried putting in a known dead battery. Left it overnight for around 10 hours but not sure if it was charging since the charge indicator showed 100% still. Same issue, turns off immediately after unplugging from wall whether there's a load or not.
Tried putting in a fully charged working battery from another UPS, same issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-01-13 07:04 AM
The hardware will need to be repaired, retired, or recycled. You may consider using this APC Resource link relating to the trade-ups program:
https://www.apc.com/shop/tradeups/us/en/search
Its a good way to recycle while getting a modest discount on a new UPS system.
Questions Ask . . . đź‘Ť
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.