Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Feedback Needed! UTS10BI & eu2000i

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Feedback Needed! UTS10BI & eu2000i
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Sifter_apc
Crewman Sifter_apc
Crewman

Posted: ‎2021-06-29 10:36 PM

0 Likes
6
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

Feedback Needed! UTS10BI & eu2000i

This was originally posted on APC forums on 7/26/2012


Has anyone actually installed this combination and have it working???

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • apc
  • eu2000i
  • honda
  • uts10bi
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
doofoo_apc
Ensign doofoo_apc
Ensign

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This was originally posted on APC forums on 8/7/2012


I went through this as well as I only have a 120V Inverter generator. I had to use a UTS6H which was a pain to get ahold of.

See Answer In Context

Reply
Replies 6
rhunter81005_apc
rhunter81005_apc
Cadet

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This was originally posted on APC forums on 4/9/2014


You CAN use an EU2000 with the UTS10BI.  While it's true that the UTS10 wants 240V on the utility side, and it will not power up with a split 120V  from the EU2000 on backup 1 (generator input), it WILL run with a UPS connected to backup 2.  You must use a UPS for this to work.  If the power goes out, UPS keeps the electronics in the UTS hot.  I took a single phase 120V source, doubled the hot legs into the backup 1 input and the "generator" input was recognized.  Now, that being said if you do this, you best not try to power anything on the 240V circuit.  I decided on this UTS because it had 8 120V circuits available while the UTS6H only has 6.  I have no 240V devices in my house, so this works great for me.  In theory you can use circuits 9 and 10 as 120V as well if you want but only if the "generator" is running, not the UPS.  My deal was that I wanted the ability to use a 220V generator later in life, and this was a great solution.

-Ryan

Reply
Sifter_apc
Crewman Sifter_apc
Crewman

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This was originally posted on APC forums on 8/30/2012


I guess its time to order an eu6500is then. I got my UTS10BI on the cheap, $250, so not going to replace it with a 6 circuit model just to accommodate my eu2000i.

Electrician was here last week and installed the unit. I have an APC Smart-UPS 2200 battery backup configured as backup2, and the outdoor plug is made by Reliance.

Attachments
Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This reply was originally posted by Angela on APC forums on 8/1/2012


hello,

the EU2000I is only a 120V generator and the UST10BI is 240V so I am thinking it'd have to run from the Backup1 (generator) source..? am I making any sense?

Reply
Sifter_apc
Crewman Sifter_apc
Crewman

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This was originally posted on APC forums on 8/7/2012


Can you explain a bit more on why backup1 would be used? Would all circuits be available?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This reply was originally posted by Angela on APC forums on 8/7/2012


i went back and checked again but i am getting more feedback that this would not even work because the UTS10BI requires 240v to power on and you cannot provide it power from the 120v generator.

Reply
doofoo_apc
Ensign doofoo_apc
Ensign

Posted: ‎2021-06-29 10:36 PM

0 Likes
0
421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 10:36 PM

This was originally posted on APC forums on 8/7/2012


I went through this as well as I only have a 120V Inverter generator. I had to use a UTS6H which was a pain to get ahold of.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc