UTS6H Load Transfer Question

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H Load Transfer Question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 10:40 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
6
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:40 PM . Last Modified: β€Ž2024-03-20 01:08 AM

UTS6H Load Transfer Question

Hello,

I was wondering if I could get a little more information about the Load Transfer feature of the UTS6H. The manual only mentions this feature briefly as an option in the UTS Configurable Features table list but does not go into any details. I am trying to decide if this feature would be worth getting a UPS.

First I want to say that I do not plan to use the uninterruptible feature of the UTS because the loads that I would want to be uninterruptible are on branch circuits with many other types of loads and do not want this branch circuit to be powered from Circuit 1 all the time as indicated in the manual.

However I can see the usefulness of using a UPS as a temporary load share if needed. So how does this work? I'm assuming the "Either" setting would have to be selected in the Circuits Setup? What happens to these selected loads when utility power fails? Will the UPS power these loads immediately or would the generator need to be started before the UPS can be used?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

Thanks again for the reply. πŸ™‚ This is a very cool transfer switch and I hope it's a big seller for APC. It's only down side that I can see might be its size, but this is not an issue for my installation. Thanks again for answering my question.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 10:40 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:40 PM . Last Modified: β€Ž2024-03-20 01:08 AM

hello, personally i am a little rusty on UTS questions so I asked someone who deals with it more frequently. here are some questions/comments:

is it possible you are confusing load shed and load transfer? The transfer is just referring to the UTS and how it will transfer the power from utility to UPS to generator. If you doesn't want to have uninterruptible circuits and don't want to have the generator auto start, then a UPS is not needed. The load shedding would be more of turning off and on non essential circuits if it looks like the load may overload the generator (one of the reasons you have to set the generator capacity in the UTS).

let us know if we misunderstood or if you have further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

Thanks for replying.. I think you misunderstood. I understand that "Load Shed" is shutting down a circuit. On page 3 of the Operation Manual currently available on the APC site, "Load Transfer" is listed, along with Load Shed & Time Management, as a feature under the UTS Configurable Features table stating, "Provides automatic transfer of select loads between a generator and a UPS". I'm assuming this means the UTS can switch a load (with the exception of circuit1) from the generator to a UPS if it determines the generator is close to overload in order to minimize power interruptions. Also assuming that selecting "Either" in the Circuit Setup will enable this behavior but I'm not positive because there is no other mention of "Load Transfer" anywhere else in the manual.

My question is what happens to a circuit programmed as "Either", not "Uninterruptable" (meaning, can be powered from a generator or UPS) when utility power fails. My generator is manual so will not be available when utility power fails until I set it up. Will that circuit, programmed as "Either", be switched to a UPS (with the understanding there might be a power interruption) or will this type of load transfer only occur if a generator is running but close to overload, when a Load Shed might occur?

The owner's manual is very thorough and well written but information is sparse regarding this feature.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

Thanks again for the reply. πŸ™‚ This is a very cool transfer switch and I hope it's a big seller for APC. It's only down side that I can see might be its size, but this is not an issue for my installation. Thanks again for answering my question.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

ok, did some more research with some folks here.

You are correct in that setting the circuit to either will allow the UTS to auto select the source for that circuit, which would aide the unit during Adaptive Load Management. In a case where the generator is unable to provide adequate power to the load, the UTS can switch one circuit to UPS instead of having to "delay" it or turn that circuit off.

Now, the only way the circuit will receive power while the UTS is switching between utility and generator is if the circuit is set to Uninterruptable. The either or UPS setting will not do this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

Thanks again for the reply. πŸ™‚ This is a very cool transfer switch and I hope it's a big seller for APC. It's only down side that I can see might be its size, but this is not an issue for my installation. Thanks again for answering my question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

0 Likes
0
968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 10:41 PM . Last Modified: β€Ž2024-03-20 01:08 AM

Thanks again for the reply. πŸ™‚ This is a very cool transfer switch and I hope it's a big seller for APC. It's only down side that I can see might be its size, but this is not an issue for my installation. Thanks again for answering my question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of