F05 error
  • Re: F05 error
  • Subscribe to RSS Feed
2150
83
Techie_apc
Sisko Techie_apc
83
Chris22
Chris22
Posted: ‎2023-12-01 11:44 AM
5514
F05 error
I have a Back-UPS Pro 1500 that powers on and then displays a F05 error for a few seconds and immediately shuts off. Is this a battery issue or something more involved?
MikeV
Ensign MikeV Ensign
Posted: ‎2023-12-10 06:25 PM
1
5492
Hi @Chris22
F05 pertains to a Charger Fault. Unfortunately, this is not user replaceable. The UPS needs to be replaced. You may want to reach out to your local support should you need further assistance.
https://www.apc.com/us/en/country-selector?ref_url=/us/en/support/
Replies 4
MikeV
Ensign MikeV Ensign
1
5493
Hi @Chris22
Chris22
Chris22
Posted: ‎2023-12-12 12:23 PM
In response to MikeV
Thanks Mike, I suspected as much when I pulled the battery and found liquid inside. Not sure if something was spilled or if that was from the battery? Either way, it's going to e-waste.
bldufour
bldufour
Posted: ‎2024-05-13 01:18 PM
Hate to disagree, but all I did was change battery and voila, no more error.  To test, I put bad battery in another SmartUPS Pro 1500 and got same error.
bldufour
bldufour
Posted: ‎2024-05-13 01:20 PM
Hate to be contrarian, but I took the battery out of my Pro 2500 that had the error and put it in another.  Error followed battery. Bought new battery and tested in both units.  No error.  My 2 cents, it is the battery.