Hello,
Up until yesterday everything was fine.
Yesterday: I hear a high, steady beep. I walk over to my PC. It is dead. The 1500 XS has the message "F01" on it and, again, it has a steady beep. I press the power button - it shuts off. I turn it back on. Battery light is empty and blinking. Start up my PC and all is fine for the next 24 hours. This morning around the same time it does the same thing. Is this some sort of battery test that runs every 24 hours? Has my battery reached a point where it no longer can support my 850 watt PC PSU, or is this some sort of power spike that is hitting every 24 hours starting yesterday? Nothing has been added to the UPS.
Any ideas? Any suggestions would be great!
Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:41 AM . Last Modified: 2024-03-21 10:58 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:41 AM . Last Modified: 2024-03-21 10:58 PM
Rob,
If you have a XS1500 the maximum load is 865 watts. We recommend keeping the unit at or below 80% of maximum load or 692 watts.
How old is the battery? At the load you are running the UPS should not be overloaded.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:41 AM . Last Modified: 2024-03-21 10:58 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:41 AM . Last Modified: 2024-03-21 10:58 PM
Rob,
If you have a XS1500 the maximum load is 865 watts. We recommend keeping the unit at or below 80% of maximum load or 692 watts.
How old is the battery? At the load you are running the UPS should not be overloaded.