Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ES series 360 va 200watts up to 27 minutes I think I have a problem

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: ES series 360 va 200watts up to 27 minutes I think I have a problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
13
2500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

ES series 360 va 200watts up to 27 minutes I think I have a problem

Backs-UPS ES 350 firmware 823.B.1.D PowerChute personal edition 2.2, I have windows 7

Had this from 2007 never really had problems until couple of years I have gotten, clicks here and clicks there then (recharging) or power in on run on power while I notice it shows "blackout" while I didn't had one.. When there was a black out I would get a message about going to hibernation all the time when something happens, and I am suppose to have 35 mins but I get hibernation really fast..

There was times I would vaccum then the power would shut off circuit breaker but my computer shuts off too including apc 3 times it did this, so tonight while I was playing world of warcraft while two fans are going including two things I forget it's called it sucks up the water from the air because the rug has water in it.. So the power in the basement shut off including my pc and apc battery too, so after a while I did a test I had the screen of apc powercute personal edition on, I took the plug out of the outlit and saw the power went to 35 to 18 then 1 hibernation like in 1 min..

I sometimes get the message about the battery needs to be replace but I have always got that even a month while I had it, but I always turn it off then reset it, then I could see the mins back.. But whats the point in having a battery if it doesn't even if you time to save your work or something? I mean using a laptop and power go's out it runs on the battery still and you have a hour..

I apologies to the people who had a hard time reading thank you for your time.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Well, I'm no Windows expert, but I searched the error message you have on Google and lots of other people seem to be having the same problem - their computers are powering off as well, apparently unrelated to power sources. I found one topic on the [Microsoft support forums|http://social.technet.microsoft.com/Forums/en-US/itprovistasp/thread/51207cfd-f5b6-4541-851d-783f9e8...]. I suppose it's possible the problems you're seeing aren't caused by the UPS so I would suggest you get that issue resolved and see if you have any other issues with the UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Backs-UPS ES 350 firmware 823.B.1.D PowerChute personal edition 2.2, I have windows 7

Had this from 2007 never really had problems until couple of years I have gotten, clicks here and clicks there then (recharging) or power in on run on power while I notice it shows "blackout" while I didn't had one.. When there was a black out I would get a message about going to hibernation all the time when something happens, and I am suppose to have 35 mins but I get hibernation really fast..

There was times I would vaccum then the power would shut off circuit breaker but my computer shuts off too including apc 3 times it did this, so tonight while I was playing world of warcraft while two fans are going including two things I forget it's called it sucks up the water from the air because the rug has water in it.. So the power in the basement shut off including my pc and apc battery too, so after a while I did a test I had the screen of apc powercute personal edition on, I took the plug out of the outlit and saw the power went to 35 to 18 then 1 hibernation like in 1 min..

I sometimes get the message about the battery needs to be replace but I have always got that even a month while I had it, but I always turn it off then reset it, then I could see the mins back.. But whats the point in having a battery if it doesn't even if you time to save your work or something? I mean using a laptop and power go's out it runs on the battery still and you have a hour..

I apologies to the people who had a hard time reading thank you for your time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Couple of things to point out before we begin:

a) You have the smallest UPS that APC manufactures.
b) You've been getting (and ignoring?) replace battery messages.

These two points alone indicate you're not going to get much runtime. On top of that, these UPSes are not designed to provide hours' worth of runtime. A desktop is not a laptop and draws much more power than one, so you shouldn't be expecting more than 5-10m of runtime in general.

Additionally, I'm not sure what exactly is connected to it - whether that includes these "fans" and "water sucking devices" (dehumidifier...?) - but you're playing WoW on this computer that presumably IS connected, and this tiny UPS isn't really designed to handle gaming rigs. Again, WoW isn't the most demanding game and I don't know if this is a high end system or not, but the UPS is more designed for the lowest of the low end computers, really, so still worth mentioning.

On that note, the basic communication this UPS family utilizes isn't the most accurate when it comes to runtime. Yes, the load will fluctuate which will influence your expected runtime, but the simple signaling isn't the best at detecting and adjusting to these changes.

Now on to more detailed info, since like you suggested, I had trouble understanding your post. To clarify, the UPS seems to be going to battery legitimately, in response to breakers tripping in your home - so that part sounds like normal functionality (for the UPS at least). However, your issue is with the fact you have little to no time to react to said outages. Does the UPS beep when this happens? Are there any flashing lights? Does it immediately turn off or does it give you a minute or two? What is the unit's model & serial number?

Either way, really, I suspect you at least need a new battery and more reasonably, a larger UPS. You might be interested in APC's [Trade-UPS program|http://buy.apc.com/commerce/storefronts/tradeups/tradein.aspx], since a new battery usually isn't that much cheaper than a new UPS, and this way you'd get a discount on a new unit and prepaid disposal of the old one.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

buzz I do apologize that you had trouble understanding me, but thank you for really making a effort.. I will answer your questions then making a big post.


dehumidifier, fans and pc's were on one, so the breaker just stop working for a moment.. Thats when the pc shut off with out making a noise, the battery shut off too no blinking lights..

Beeping of the battery: While I unplug the battery there are beeps to let me know it's running on power, including it flashs green..
Replace battery message: The apc doesn't show a red color on replace battery, infact it has always done this gave me a message sometimes... I remember for a month having it and still gave me the message.
immediately turn off: yes it does sometimes while I am using the big industatal vaccum, the power would shut off including the apc batterie..
Plugs I am using battery back up & surge protection: I have my linkeys router plug on the surge protection, pc & monitor plugs are on the battery back up.
Surge protection only: I am using my modem for that.
Model number&serial number: BE35OR / 3B0732X17258
Monitor: syncmaster 941v samsung LCD I think it's a 17 or 15 inch
Pc tower: 32bit, win7, I have chasm fan and a motherboard fan.
35 mins: it go's really fast like 35min 20 min 19 min then 1min after gives the window of hibernation..

Could something be wrong with my apc battery?

Message was edited by: keithnerdloveapc

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

What version of PowerChute Personal Edition are you running? I assume it's the latest one for Win7, v2.2, but it's always good to check.

In that version, if you go to Monitor System > Current Status, does it list the battery capacity and/or the load on the battery backup? It may not report the latter, I'm not sure this small unit has that info...

It would probably be faster/easier for you to call tech support (800-890-4272) and troubleshoot the unit with a technician to determine what the issue is - whether it's the unit, the battery, or something else. The load may be too much for this little UPS to handle, but by troubleshooting you should be able to figure it out and decide what action to take from there. It's kind of difficult to do via posting but it's up to you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

in addition buzz suggestions, would like to add some more points on this issue....

Each model of Back-UPS is capable of handling up to a certain amount of equipment. The UPS runtime depends upon the equipment connected to the battery backup outlets.This UPS estimated battery runtime is 9.7 minutes at 100 watts and 2.3 minutes at 200 Watts. The correct runtime will not be calculated properly with the Back UPS ES 350 unless the unit is on battery. After operating on battery for brief periods of time, it calibrates the UPS to reflect the runtime more accurately. Depending on the power factor of the computer system, the runtime may be a little lower than expected.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Secondly, you may also do a pull plug test to see if the unit provide the correct runtime. this unit normally provides 9.7(appr.) at 100 Watts load. Please charge your unit for 8-10 hours continuously with out any load and connect a non critical load like a lamp, with a watt rating between 60-100 Watts. Then disconnect the UPS from the wall outlet and check the runtime manually. this test will help you to understand the root cause of your concern.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

I have done that before same results, 36, 20m 19m 1min.. Would it be the battery it self or the apc I have is old?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

I don't think anything is wrong with the UPS itself. It's almost 3 years old and the batteries usually last 3-5 years. However, based on what you're describing, it doesn't sound like anything is necessarily broken. You're just expecting this tiny unit to give you a lot more runtime than it's able to.

You said you "already did" the test Techie suggested - what wattage light bulb did you use then? And he said to check the runtime manually, that means measure how much runtime you get outside of what PCPE is saying you'll get. Like he said, it takes a minute for the runtime to update after it's on battery.

If you want more runtime, you just need a bigger unit. They're really designed just to give you a couple of minutes, and like I said before, you have the smallest unit APC manufactures. You can't expect to get the functionality of a $200 unit with a $50 unit.

That's why I suggested the Trade-UPS program... That way you can get a discount on a larger unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

buzz is there somewhere that could explain to me what you just mention because it went way over my head.. Still as you suggestion I should call apc about this..

So a laptop uses less batterie then a destop does?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Yes, most definitely. A laptop's components are designed to function for awhile (typically an hour or more) on its own internal battery, so the laptop components typically draw much less power than a desktop's would. That's the whole point of the laptop - portability, and not always being reliant on the power outlets available.

I can try to think of a few examples to compare to give you a better idea of how it works... Think of a truck engine compared to that of a little tiny compact car. The truck typically uses more fuel than the little car would because it's bigger and requires more power to move it. The same idea goes for a desktop compared to a laptop. The laptop requires less power, so it will run longer on the same size battery, much like the smaller car can go further than the truck on the same tank of gas.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Thank you buzz for explaining that I would of understand.. I just wish the guy from stapples told me, because he said that my pc would last 36 mins before it shuts off that I told him it's a pc that I am using it for.

So about the battery that giving me a warning sometimes, I haven't got the warning stopped on the 18th. What I don't understand why I have gotten the pop up message but never the replace the batterie showing red or why the batterie just stopped when the whole downstairs got shut off..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Buzz I have a question thats related to my upc batterie, I don't know if this is indeed related I get a randomly freeze.. While looking at the event viewer after coming back on I get this (Some processor performance power management features have been disabled due to a known firmware problem. Check with the computer manufacturer for updated firmware.) then it wouldn't do a randomly freeze but I get that message all the time...

I already ask this question from another site just wanted to see if this is related thats all.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

0 Likes
0
2499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:04 AM . Last Modified: ‎2024-03-22 02:17 AM

Well, I'm no Windows expert, but I searched the error message you have on Google and lots of other people seem to be having the same problem - their computers are powering off as well, apparently unrelated to power sources. I found one topic on the [Microsoft support forums|http://social.technet.microsoft.com/Forums/en-US/itprovistasp/thread/51207cfd-f5b6-4541-851d-783f9e8...]. I suppose it's possible the problems you're seeing aren't caused by the UPS so I would suggest you get that issue resolved and see if you have any other issues with the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.