ES 700 Not working as expected (Newbie alert)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • ES 700 Not working as expected (Newbie alert)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
5
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

ES 700 Not working as expected (Newbie alert)

Newbie alert, first post alert.

Because of short blackouts where I live here in the UK I bought a UPS ES 700 for my computer,

Installed it as per the instructions, including the Powerchute software and all reports OK. I'm running Windows 8.1. The PC is plugged into the master socket and 2 monitors and an external drive into the other three protected sockets. Estimated battery time shows as 31 minutes.

The software is set to stay on as long as possible shutting down when backup power is 8 minutes.

Just had my first power outage. The alarm starts bleeping then everything just goes off after around 5-10 seconds. No controlled shut down.

The PowerChute performance tab has recorded the incident but shows the time on battery as 'None' See below

%2B%2B7wF5kBrvBoTxQnmVxhlQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg%2B%2B7wF5kBrvBoTxQnmVxhlQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Just to check I disconnected the computer and connected a table lamp instead and turned the power off. The alarm sounded and the lamp stayed on.

Any advice out there please?

Thanks in advance

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

Hi,

The runtime chart shows at 31 minutes there should be a 100 watt load. You wrote that there are 2 monitors, 1 PC and a hard drive being powered. What wattage do the monitors draw? You will find that info from the manufacture. You should also find out what the PC should be pulling during normal operation and what the hard drive pulls. 

if the load is only 100 watts the UPS should not drop based on load. One thing that may cause the PC to power down would be mismatch with the UPS sinewave. Some PC do not like the Back-UPS sinewave but that issue would only cause the UPS to power down not the monitors and hard drive. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

Hi,

It sounds like the unit is going into overload when transferring to battery based on the description. What is does PowerChute report the load is with all equipment connected?  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

Thanks,

However, I can't find the 'load' on the Powerchute (Personal Edition). Is this just on the business software?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

Hi,

You will find the load information under Current Status.

PWco0c2i7oYYC5m5HIZ7ZA%3D%3D.pngPWco0c2i7oYYC5m5HIZ7ZA%3D%3D.png 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

Many thanks for coming back to me but not in my version PowerChute Personal Edition 3.0.2

GOv406bxAcEj%2FTDunFXx1w%3D%3D.jpegGOv406bxAcEj%2FTDunFXx1w%3D%3D.jpeg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-26 10:48 PM

Hi,

The runtime chart shows at 31 minutes there should be a 100 watt load. You wrote that there are 2 monitors, 1 PC and a hard drive being powered. What wattage do the monitors draw? You will find that info from the manufacture. You should also find out what the PC should be pulling during normal operation and what the hard drive pulls. 

if the load is only 100 watts the UPS should not drop based on load. One thing that may cause the PC to power down would be mismatch with the UPS sinewave. Some PC do not like the Back-UPS sinewave but that issue would only cause the UPS to power down not the monitors and hard drive. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore