Hi all,
I have an APC EASY UPS BVX 900 LI-IN, and I’m facing a strange issue:
When running on battery, it shuts off exactly after 2 hours, every single time. This happens even if:
So it’s not due to low battery, but seems to be a built-in timer or firmware limitation.
I’d like to disable or extend this 2-hour limit. It’s causing problems during longer power cuts where the battery still has juice but the UPS turns off anyway.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-16 02:58 AM
If the system had a data port to connect to APC PCSS you could adjust the default runtime.
Given this isn’t an option this isn’t a choice. If you require longer operational runtime a larger UPS is the correct path to follow or one that allows extended battery packs to be added.
The RBC is rated to provide 2-5 years of service based on usage, temperature, and environmental conditions. The system is designed to shutdown before the RBC is 100% depleted as its rated to provide 260 cycles before degradation of the cell(s).