Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Do I have a bad replacement battery ? Or is my BackUPS 900 xs at fault ?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Do I have a bad replacement battery ? Or is my BackUPS 900 xs at fault ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
8
518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

Do I have a bad replacement battery ? Or is my BackUPS 900 xs at fault ?

This was originally posted on APC forums on 4/19/2010


For my BackUps 900XS I got a replacement battery from a vendor called APCUPSBattery.com. I charged it to 95% and then plugged in my equipment to the battery protected sockets: the protected equipment drew a total of 280 watts while the unit is rated at 540w.

Ten hours later the PowerChute software showed the battery was charged only 15% and then three hours later on the software showed a charge of 0%. At that point in time, the BackUPS 900 unit passed the PowerChute self test.

I then unplugged all equipment and let the unit charge. When I checked a day later, the "Replace Battery" light was flashing.

QUESTION: Is this the fault of the BackUPS 900 or the new battery ? Is there anything I can do to fix it ?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • replacement
  • replacement_battery
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This was originally posted on APC forums on 4/19/2010


For my BackUps 900XS I got a replacement battery from a vendor called APCUPSBattery.com. I charged it to 95% and then plugged in my equipment to the battery protected sockets: the protected equipment drew a total of 280 watts while the unit is rated at 540w.

Ten hours later the PowerChute software showed the battery was charged only 15% and then three hours later on the software showed a charge of 0%. At that point in time, the BackUPS 900 unit passed the PowerChute self test.

I then unplugged all equipment and let the unit charge. When I checked a day later, the "Replace Battery" light was flashing.

QUESTION: Is this the fault of the BackUPS 900 or the new battery ? Is there anything I can do to fix it ?

See Answer In Context

Reply
Replies 8
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This was originally posted on APC forums on 4/20/2010


Thanks for your response. When I installed the battery it was definitely connected, because it charged. Since then I have not disconnected it. When I ran the PowerChute self test on the UPS, the UPS passed the self test. Given these facts, what does the "Replace Battery" light mean ? Could the UPS be bad (even though it passed its own self-test), or does it mean the battery is bad ?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This reply was originally posted by Jonathan on APC forums on 4/21/2010


Robert,

By any chance do you have an APC original battery that is compatible with your UPS? From your first post you have stated that you bought the battery from APCUPSBattery which is not connected to APC. I think what they offer are batteries that are compatible with our products as well as with other manufacturers.

Regarding your question about the Replace Batter LED, when this LED is lit up solid it means that the UPS has failed the self-test and the battery inside it is bad and needs to be replaced. If that LED is flashing, it means that the UPS doesn't detect any battery connected to it. This could be due to installation of a non-APC battery or the sensor on the UPS has gone bad. If you could find a working APC battery that is the same as with your UPS, it would help if you can connect it on this UPS.

JonPro

Reply
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This was originally posted on APC forums on 4/21/2010


Thanks for the reply, Jon. Unfortunately I don't have a known good battery to test whether the UPS is working.

Further development: after declining to 0% power remaining, and then going to the battery replace light, the UPS is now showing no lights whatever when plugged in to the wall.

Thing that puzzles me is the new battery initially charged to 95%, suggesting it was recognized by the UPS as a valid battery, and the UPS passed the software self test with that battery present: subsequently it declined to 0%, declined further to "Replace battery", then declined further yet to showing nothing at all, all within about 48 hours.

I guess my underlying question is whether the observed behavior looks like bad battery or bad UPS or is ambiguous.

Thanks again for your reply.

P.S. I contacted APCUPS.com and they were very helpful and agreed to send a replacement. So I'll have to wait for it to arrive and see whether it works or not.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This reply was originally posted by Jonathan on APC forums on 4/21/2010


Let us wait and see what happens with the battery that they'll be sending. In the future, please make sure that you only purchase APC products from us or from authorize resellers. If the new battery won't fix the issue, I suggest that you look for an APC battery if not you can avail of a new UPS with discount via TradeUPS.

Reply
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This was originally posted on APC forums on 4/23/2010


I received replacement batteries yesterday. I checked them with a meter and the needle was in the "Battery Good" zone. The batteries are "TOYO-USP 6FM9 F2 (12V 9AH/20HR), Sealed Rechargeable Battery, Constant Voltage Charge," dated 0204 10, which looks like February 4 2010, implying they are new. I installed them in the BackUPS 900 XS and started charging them 6pm April 22 and checked 9am April 23. The PowerChute personal edition software reported battery capacity of 56% at 9am, declining to 37% at 3pm. When I turned on the UPS at 9am it passed the self test, both software, and hardware (flashing green for awhile, solid yellow for awhile, then solid green). At 3:39 it again passed the self test, even though the batteries had been steadily losing charge. Any idea why this was happening ?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This reply was originally posted by Jonathan on APC forums on 4/26/2010


With the replacement batteries installed, did the replace battery LED stopped flashing?

If you cannot really test it with a Genuine APC battery and it keeps doing this, I suggest that you replace the unit itself. There's a possibility that the charging mechanism on the unit is not functioning properly. You can call our APC Technical Support if you are in the U.S. and ask for TradeUPS to avail a discount on the UPS that you would like to have.

JonPro

Reply
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This was originally posted on APC forums on 4/26/2010


With the replacement batteries installed, did the replace battery LED stopped flashing?

Yes, the replace battery LED stopped flashing as soon as the replacement batteries were installed. However, the replacement batteries failed to retain their charge, and declined to zero capacity over 18 hours, despite the fact the UPS passed its own self-test.

Reply
boblite2_apc
Ensign boblite2_apc
Ensign

Posted: ‎2021-06-29 08:59 PM

0 Likes
0
520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:59 PM

This was originally posted on APC forums on 4/19/2010


For my BackUps 900XS I got a replacement battery from a vendor called APCUPSBattery.com. I charged it to 95% and then plugged in my equipment to the battery protected sockets: the protected equipment drew a total of 280 watts while the unit is rated at 540w.

Ten hours later the PowerChute software showed the battery was charged only 15% and then three hours later on the software showed a charge of 0%. At that point in time, the BackUPS 900 unit passed the PowerChute self test.

I then unplugged all equipment and let the unit charge. When I checked a day later, the "Replace Battery" light was flashing.

QUESTION: Is this the fault of the BackUPS 900 or the new battery ? Is there anything I can do to fix it ?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc