Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Cryptic Smart UPS C1500 Configuration. What do these codes mean?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Cryptic Smart UPS C1500 Configuration. What do these codes mean?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
vinnysaj
vinnysaj
Explorer

Posted: ‎2024-11-22 04:32 PM

1 Like
2
4386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-22 04:32 PM

Cryptic Smart UPS C1500 Configuration. What do these codes mean?

The Smart UPS C1500 has a very limited screen, so the cryptic configuration names are expected, but I cannot find any information in the manual about some of the configurations. Specifically, I want to calibrate my battery and enable smart connect control.

 

SE.0 -> Performs a self test when set to SE.1, I am pretty sure

P9.3 -> Sensitivity setting

dP.1 -> Unknown

cP.0 -> Unknown

Gn.0 -> Green mode (0 off, 1 on)

rc.0 -> Unknown

rb.0 -> Unknown (Has a battery with X symbol. Unknown what this is)

cod -> This switches between multiple codes, but I left it as this because I have no idea what any of the other codes mean

FU.1 -> Unknown

 

This UPS also only has 3 buttons, power, mute, and display. To enter this config menu you have to hold both the display and mute buttons. Mute changes the setting on-screen, and display increments through the menu.

 

I've searched between multiple editions of the manual for this unit and have not found full information as to what all of these codes mean. Wondering if anyone else here has any idea?

 

Additionally I am seeing a L.02 code which means battery must be replaced. Just replaced the battery, so assuming that I need to now run a calibration or something to get this code to go away. Knowing the configuration will let me do this.

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2024-11-23 02:18 PM

1 Like
1
4288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-23 02:18 PM

I have appended the user manual I believe you are asking about for this APC UPS. On page 11 calls out how to enter the configuration mode. On page 13 calls out how to enable the Smart Connect remote commands and also reset the battery replacement flag.

 

You should be able to enter the battery installation date via APC Power Chute software too.

 

To properly inform the system a battery has been inserted follow these steps:

 

- Update the battery installation date if available in PCBE / PCSS / LCD. Doing so resets the counters and charging tables if applicable.

 

- Self Test: Manually initiate this via LCD / PCBE / PCSS and let battery come back to 100% and online state.

 

- Battery Calibration: Initiate the battery calibration via the PCBE / PCSS software if available with at least 30% attached load on the outputs of the UPS. Let this process complete and battery to fully charge and show on-line.

 

Doing so will ensure the LCD / Power Chute software will reflect the operational runtime when on battery only mode. Keep in mind the value displayed is an estimate and does (NOT) reflect all possible environmental conditions such as load, battery health, SOC, etc.

 

Questions  Ask - If not please consider marking this reply as a solution. So it may help the next person asking the same. 👍 

 

chrome-extension://efaidnbmnnnibpcajpcglclefindmkaj/https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SU_UM_990-5444E_MN0...

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Teken
Champion

Posted: ‎2024-11-23 02:18 PM

1 Like
1
4289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-23 02:18 PM

I have appended the user manual I believe you are asking about for this APC UPS. On page 11 calls out how to enter the configuration mode. On page 13 calls out how to enable the Smart Connect remote commands and also reset the battery replacement flag.

 

You should be able to enter the battery installation date via APC Power Chute software too.

 

To properly inform the system a battery has been inserted follow these steps:

 

- Update the battery installation date if available in PCBE / PCSS / LCD. Doing so resets the counters and charging tables if applicable.

 

- Self Test: Manually initiate this via LCD / PCBE / PCSS and let battery come back to 100% and online state.

 

- Battery Calibration: Initiate the battery calibration via the PCBE / PCSS software if available with at least 30% attached load on the outputs of the UPS. Let this process complete and battery to fully charge and show on-line.

 

Doing so will ensure the LCD / Power Chute software will reflect the operational runtime when on battery only mode. Keep in mind the value displayed is an estimate and does (NOT) reflect all possible environmental conditions such as load, battery health, SOC, etc.

 

Questions  Ask - If not please consider marking this reply as a solution. So it may help the next person asking the same. 👍 

 

chrome-extension://efaidnbmnnnibpcajpcglclefindmkaj/https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SU_UM_990-5444E_MN0...

 

Reply

Link copied. Please paste this link to share this article on your social media post.

vinnysaj
vinnysaj
Explorer

Posted: ‎2024-11-24 11:09 AM

In response to Teken
0 Likes
0
4277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-24 11:09 AM

Awesome. Out of the 4 manuals I found online, none were as descriptive as this one. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore