Backups PRO 1500 S beeping, but passes all tests

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Backups PRO 1500 S beeping, but passes all tests
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
lorg00
Crewman lorg00
Crewman

Posted: ‎2024-11-21 08:33 PM

0 Likes
3
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-21 08:33 PM

Backups PRO 1500 S beeping, but passes all tests

I have a Backups PRO 1500 S. We had a big wind storm recently and the power briefly went out. My attached computer was in sleep mode. I tried to power the Backups off, causing the unit to throw an F02 error before it shut down.

Everything about the unit currently seems to be fine: the battery charged fully, it has passed self-tests both through the power button and through PowerChute Personal Edition software. But every 5 hours, it goes into beeping mode. I have twice tried powering the computer and monitor off, disconnecting everything, shutting the Backups off, disconnecting its battery, giving it a couple minutes, then reversing the process. It still powers up fine, seems to function fine, but continues to do a beep cycle every five hours, or any time the power glitches.

 

I'm not pleased that the self-test cannot report an error, but the problem persists. How do I determine what is wrong, and how do I fix this?

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Spock Teken
Spock

Posted: ‎2024-11-22 06:20 AM . Last Modified: ‎2024-11-22 06:21 AM

0 Likes
0
275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-22 06:20 AM . Last Modified: ‎2024-11-22 06:21 AM

You’ll need to review the event and data logs to see what are the active faults / errors.

 

Provide both data & event logs for review here. The vast majority of problems will be captured and displayed on the LCD.

 

When the unit beeps go to the LCD and confirm the current state, input voltage, output voltage, frequency, etc.

 

If you see the AVR indicator on during this time it simply tells you the system is working as expected by trim / boosting the output.

 

If you see the system is not online but in battery only mode. Again, it’s working properly by switching over to battery to provide cleaner power as the input is considered dirty. 

As an aside a F02 is a connected short. Meaning there is something wrong with the attached load or the UPS has an internal fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

lorg00
Crewman lorg00
Crewman

Posted: ‎2024-11-22 07:15 PM

0 Likes
1
244
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-22 07:15 PM

I'm not sure what you're talking about.  There are no "event and data logs," it's a UPS.  The display shows that one event occurred, though that might be new, but apparently one cannot dive any deeper than that on the display.  The PowerChute software shows nothing, and has no capacity for data logs.  It has a one-page display that shows some general event information, that's all.  See attached.

Frankly, the unit design is a disappointment in terms of providing useful diagnostic information.  

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-11-25 06:08 AM

In response to lorg00
0 Likes
0
241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-25 06:08 AM

Each of the tabs will show different data and metrics. Show me each tab once select.

 

As a reminder the software will only capture information while the computer is attached to the UPS and on.

 

This specific model does not have enough on board memory to store all the event’s except critical faults.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of