Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Complete Smart-UPS 2200 Shutdown When Battery Reaches Low Runtime (900 seconds) and Auto-Restart on Power Restoration

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Complete Smart-UPS 2200 Shutdown When Battery Reaches Low Runtime (900 seconds) and Auto-Restart on Power Restoration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Maxim
Maxim
Explorer

Posted: ‎2024-09-13 05:17 PM

0 Likes
1
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-13 05:17 PM

Complete Smart-UPS 2200 Shutdown When Battery Reaches Low Runtime (900 seconds) and Auto-Restart on Power Restoration

Hello,

I am using a Schneider Electric Smart-UPS 2200 with UPS Network Management Card 2 (AP9631), firmware version UPS 09.4 (ID18). I am located in Ukraine, where frequent power outages make it critical to properly manage the UPS behavior.

Problem: I would like the UPS to completely shut down when the battery runtime reaches 15 minutes (900 seconds) to prevent further battery degradation. However, I also need the UPS to automatically restart when power is restored.

In the Network Management Card 2 settings, I have configured the Outlet Group to turn off the load when the battery runtime drops below 900 seconds. However, the inverter continues to run and further discharges the batteries, which I want to avoid. There doesn't seem to be a direct option in the current settings to fully shut down the UPS and prevent deep battery discharge.

Could you advise on how I can configure the UPS to:

  1. Completely power off when the remaining runtime drops to 900 seconds?
  2. Automatically restart the UPS when power is restored?

Any guidance or information about firmware updates or additional settings that would help resolve this issue would be greatly appreciated.

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
RyanG32
RyanG32 Contributor
Contributor

Posted: ‎2024-09-16 05:32 PM

0 Likes
0
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-16 05:32 PM

Hope that you guys are hanging in there based on the settings that you mentioned this is what you should have on all outlet groups 

RyanG32_2-1726532513871.png

the SMT2200 unit has multiple outlet groups and if you only configured the outlet group 1 the main outlet group will still run if you configure the main outlet group to turn off then both outlet groups should power down.  The green outlets can be powered off without powering off the Main outlet and the Main outlet groups once powered off will turn off all outlets make sure that you configured at least the Main outlet group of the both of them.

RyanG32_3-1726532649541.png

also make sure that the option to stay off after power returns is unchecked so that UPS automatically restarts.

 

You can also use the Minimum Return Runtime to make sure that the UPS has enough  runtime before powering on.

 

 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore