Charger voltage are too low

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Charger voltage are too low
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
12
7635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Charger voltage are too low

Hi

I am facing charging issue in BX650CI UPS. The charger voltage are too low i.e.8.3VDC. According to my understanding it should be near about 14VDC.

I have swap the battery with new one but issue not resolved.Kindly look into it. Snap attached.

Mukhtar Ahmad

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Yes, if the UPS was healthy you should definitely be measuring at least 13.5 to 14 volts at those spade terminals. Are you feeding the UPS the correct input voltage (and frequency) ? (looks like 230 volts AC ?). With the battery plugged in do any fault indicators light up as you power up the UPS and it does its self test ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Thanks for reply.

Yes. 228VAC and 49.98Hz. When charged battery plugged it is working fine but when take some backup battery low and not charged for next.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

As a better test, I would measure the output voltage of the charger with it connected to the battery, NOT with the leads disconnected, as you show in the photo. Allow sufficient time for the battery to charge / recharge. From a deep discharge it may take several hours to reach 13.5 volts or more, I don't know what this UPS specifies for recharge time. If after running the UPS on battery for several minutes with a modest load (say 10 minutes with 100 watts) the battery returns to more than 12.5 volts after restoring AC power I would say your charger is operating, and your 8.3 volt reading is invalid. Again, it will take time to recover to the maximum voltage, close to 14 volts, and even then more time to charge to full capacity.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Hi

I am facing charging issue in BX650CI UPS. The charger voltage are too low i.e.8.3VDC. According to my understanding it should be near about 14VDC.

I have swap the battery with new one but issue not resolved.Kindly look into it. Snap attached.

Mukhtar Ahmad

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Yes, if the UPS was healthy you should definitely be measuring at least 13.5 to 14 volts at those spade terminals. Are you feeding the UPS the correct input voltage (and frequency) ? (looks like 230 volts AC ?). With the battery plugged in do any fault indicators light up as you power up the UPS and it does its self test ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Thanks for reply.

Yes. 228VAC and 49.98Hz. When charged battery plugged it is working fine but when take some backup battery low and not charged for next.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Unfortunately from what you report it sounds like the UPS has an internal fault. This fault may even be going undetected by the UPS self-testing process when you have a fresh battery connected ?

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

As a better test, I would measure the output voltage of the charger with it connected to the battery, NOT with the leads disconnected, as you show in the photo. Allow sufficient time for the battery to charge / recharge. From a deep discharge it may take several hours to reach 13.5 volts or more, I don't know what this UPS specifies for recharge time. If after running the UPS on battery for several minutes with a modest load (say 10 minutes with 100 watts) the battery returns to more than 12.5 volts after restoring AC power I would say your charger is operating, and your 8.3 volt reading is invalid. Again, it will take time to recover to the maximum voltage, close to 14 volts, and even then more time to charge to full capacity.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

I've worked with almost the entire line of APC ups and cannot recall one amongst these smaller line interactive models that doesn't present full charging voltage to the battery terminals with no battery connected......but perhaps someone from APC could clarify/confirm for this particular model.  The recharge time on this model is stated as 8 hours.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

One other thing to check would be that the UPS's rear panel "Battery Connector"  (...its at the upper right hand corner of the back panel ) to make sure its terminals are in good condition and not weak/loose.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

Battman, I'll defer to your experience here... I was thinking of a more general case where a voltmeter will incorrectly read the average of short pulses from a more sophisticated charger. Also, there could be conditions where you could read the "proper" voltage at the disconnected terminals but still not be able to charge a battery when connected. I thought Muahmad may have overlooked (or not reported on) some diagnostic steps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:03 PM . Last Modified: ‎2024-03-20 03:21 AM

I have check the rear fuse it is OK. I would also come to you knowledge that I have one same model UPS. It is showing correct charger voltage i.e. 13.89VDC. I have also check my voltmeter it is also showing proper voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:04 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:04 PM . Last Modified: ‎2024-03-20 03:21 AM

Your only option now is either to replace the UPS or have it repaired.... if you are skilled / careful with electronics you could unplug the UPS and let it sit for a couple of days to discharge the internal components then remove the cover and check for damaged components. If you have some component damaged in the charging circuits that may reduce the voltage and not provide any charging. There might be a blown MOSFET, or possibly a failed filter capacitor in the Charging section that is dragging down or weakening the charging voltage.

Good luck !

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:04 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:04 PM . Last Modified: ‎2024-03-20 03:21 AM

Thank you so much Battman.

Tried my best to repair it. Do you have some internal diagrams. Please share if you have. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:04 PM . Last Modified: ‎2024-03-20 03:21 AM

0 Likes
0
7633
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:04 PM . Last Modified: ‎2024-03-20 03:21 AM

APC does not officially release Schematic diagrams but as is the norm on the internet some things are available if you google search for it... I have not personally come across a schematic for that particular model but you may find very similar ones architecturally in that size range that could be helpful as a guide. Very difficult to do board level repairs on ups usually a lot of damage (sometimes hidden) occurs if components blow. Good luck to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore