CS500 goes into overlaod after battery replacement

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • CS500 goes into overlaod after battery replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
3
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

CS500 goes into overlaod after battery replacement

Looks like I have an issue with another CS500 unit. I replaced the battery, turned it on with nothing connected and it went into overload. I confirmed the contacts were connected properly and retested with the same result.

This unit looks like its been dropped at some point. It has a crack in the plastic on the front face.

Hmm... thought I would try another battery and now it seems OK. Will charge over the weekend and do some testing Monday.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

I've actually seen this overload problem happen many times on the CS series. Not only the on CS500 but a lot on the CS1000 and RS1500. I think it's just a coincidence that it happened to you when the battery was replaced. We run about 40 of these units and we have that happen pretty frequently. I am pretty sure you'd have to be crazy to send one of these units out for repair, the cost of the repair will by far outweigh the cost of buying a new or a used one. I'd keep the batteries and throw out the unit. I don't think the CS units are anywhere as reliable as the Smart UPSs.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

This is an abnormal operation of the UPS. The Overload LED should not be lit with nothing load attached. I do not think that the bad battery is the root cause of the issue. You may need to consider returning the purchased new battery to reseller for refund, and replace or repair the unit in question. If you would like to consider having this UPS repaired, you would need to contact an APC Authorized Repair Center for service costs. The company name is CBM and their telephone number is 888-2FIX-UPS (888-234-9877).

We also offer a discount on brand new units with a brand new two-year or three year warranty when you trade in your old unit. Click here to know more about the APC Trade UPS program.

Have a nice day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

OK, thanks. It may just have been random luck that the unit failed with one new battery and not the other. The new battery it failed with is in another unit now and working normally. I just verified that it holds a charge and gives us reasonable offline time.

I will keep the suspect unit out of circulation and replace it.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

I've actually seen this overload problem happen many times on the CS series. Not only the on CS500 but a lot on the CS1000 and RS1500. I think it's just a coincidence that it happened to you when the battery was replaced. We run about 40 of these units and we have that happen pretty frequently. I am pretty sure you'd have to be crazy to send one of these units out for repair, the cost of the repair will by far outweigh the cost of buying a new or a used one. I'd keep the batteries and throw out the unit. I don't think the CS units are anywhere as reliable as the Smart UPSs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore