CS500 disconnect surge load, drops 2 out of 3 loads

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • CS500 disconnect surge load, drops 2 out of 3 loads
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
108
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Beddhist_apc
Crewman Beddhist_apc
Crewman

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
5
4770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

CS500 disconnect surge load, drops 2 out of 3 loads

I have here a CS500. Top port has a power strip with 2 external USB hard disks, the other 2 one QNAP NAS each. A 24-port ethernet switch was connected to the bottom (surge protection only) port.

When I unplugged the ethernet switch, the UPS dropped both NAS instantly. The external hds continued to receive power. I had to turn the UPS off and back on to restore normal operation.

Is this normal? My confidence in the UPS is shattered.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Beddhist_apc
Crewman Beddhist_apc
Crewman

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
4771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

I removed the battery and found a little bit of corrosion on one terminal and the plug on the other was a little loose. After cleaning up both I ran a test with a 60W light bulb and a voltmeter, not connected to the UPS. In 10 mins the voltage went from 12.57V to 12.31V.

With the battery installed and charged again I ran another test with the original equipment and it lasted 3:40.

It seems to me that either the equipment draws a lot more current than Powerchute tells me and what I have worked out from the specs, or the battery collapses under the higher load.

I would like some feedback from the experienced users here.

Thanks in advance,

Peter.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
4771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

Hi Peter, you've indicated that when the 24-port Ethernet Switch was removed from the "Surge Only" receptacle the QNAP NAS both turned off. Were these two devices also connected through a surge strip to the back of the UPS? Please reference the following FAQ related to the use of Surge Protectors between the attached load and the UPS. The loads cycling off as you've described is not normal, however when a secondary surge device is added, it is difficult to say how the UPS will respond.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Beddhist_apc
Crewman Beddhist_apc
Crewman

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
4771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

Hi Secret Squirrel,

Thanks for your reply.

No external surge devices are involved. But I'm sorry, I made a mistake in my initial report. Here is the actual config:

Top port empty

Ports 2 & 3 one QNAP NAS each

Bottom port (surge protection only): ethernet switch.

The power strip was actually connected to a wall socket, so no surprise they kept going. That makes more sense now, as I can't see a low-end NAS having separate circuits for the 3 sockets.

When I pulled the switch plug both NAS lost power instantly. The UPS didn't beep and only the green light was lit. Pressing the reset button for the circuit breaker also did not help. Power off and on did.

Kind regards,

Peter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Beddhist_apc
Crewman Beddhist_apc
Crewman

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
4771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

The configuration has now changed: top port is shared by the switch and the external drives and a PC (headless). NAS on 2 & 3.

Strike 2: just after midnight our RCD seemed to think now was a good time to trip for no apparent reason, cutting power to the entire house, of course. It's not the first time this has happened.

WinNUT running on the PC logged the power failure at 00:43:48. 11 secs later it could no longer communicate with the NAS and hibernated the PC.

Both NAS logged the power failure, but no more until restarted, at which point they complained about improper shutdown, needing file system check.

By the time my wife had woken me up (she had the privilege of sleeping next to the action!) the UPS was emitting a continuous beep and had dumped the load. I believe this indicates overload.

Now I'm wondering whether I am overloading the UPS. Here are some power figures I collected quickly:

Switch: 24W

PC Dell Optiplex 960 SFF Core i5 2500: < 90W

2 x QNAP NAS TS-431: 70W together

2 x USB HDD: 14W together

Total < 200 W. Should be well within specs.

WHY then is this giving me so much grief? Does a load being removed (unplugged or shut down) cause a surge that trips it?

Yes, I have read the blurb about power strips, etc. How else do I connect all these plugs? The strip does have what looks like a circuit breaker with a reset button. Rated at 10A. I doubt there is surge protection circuitry in it, it's quite old.

PS: I just remembered, there ARE surge protectors in our mains supply, before and after the solar inverters. About 40-50 m cable length away and obviously on the other side of the house switchboard..

Reply

Link copied. Please paste this link to share this article on your social media post.

Beddhist_apc
Crewman Beddhist_apc
Crewman

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
4771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

More testing:

After pulling the plug it lasts only 90 secs. The product page says with a load of 150W it should last 14 mins.

Installed Powerchute on the PC. It indicates run time of < 1 minute, but it passes self test. The load is indicated ~ 150W.

So, if all the readings are correct the battery must be nearly dead. Why then does it pass a self test?

Reply

Link copied. Please paste this link to share this article on your social media post.

Beddhist_apc
Crewman Beddhist_apc
Crewman

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
4772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

I removed the battery and found a little bit of corrosion on one terminal and the plug on the other was a little loose. After cleaning up both I ran a test with a 60W light bulb and a voltmeter, not connected to the UPS. In 10 mins the voltage went from 12.57V to 12.31V.

With the battery installed and charged again I ran another test with the original equipment and it lasted 3:40.

It seems to me that either the equipment draws a lot more current than Powerchute tells me and what I have worked out from the specs, or the battery collapses under the higher load.

I would like some feedback from the experienced users here.

Thanks in advance,

Peter.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore