BK650M2-CH 使用apcupsd故障原因,不正常的必看

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BK650M2-CH 使用apcupsd故障原因,不正常的必看
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

0 Likes
0
5771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:42 AM . Last Modified: ‎2024-03-26 03:17 AM

BK650M2-CH 使用apcupsd故障原因,不正常的必看

BK650M2-CH是特供中国的产品,所以我用中文发帖,好让同样的问题的用户看到。

BK650M2-CH是BK650-CH的更新版本,乘着某东618活动终于忍不住入了个,然而连接好安装好了之后非常崩溃。
使用的linux作为主机,那么安装apcupsd肯定是必然的,版本当然是最新版本的3.14.14-2。

https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/bd-p/home-office-forum 这位哥们ye也出现l类似原因。

新机开始充电,可当电充满了之后BK650M2-CH居然自己关闭机器了,重新开启之后又是直接关闭机器了,查看日志
有明显的如下日志信息:
UPS Self Test switch to battery.
Running on UPS batteries.
Initiating system shutdown!
apcupsd exiting, signal 15

并且收到系统广播
UPS xxx initiated Shutdown Sequence
Battery time limit exceeded on UPS xxx. Doing shutdown.

那怕把timeout设置为0也没有用。

经过冒着数据盘故障的风险,仔细分析查找,发现是apcupsd 的问题,该用nut-server就好了。

具体原因分析如下:

1、满电时候apcaccess 显示STATUS为ONBATT ,也就是电池供电(不触发shutdown才奇怪。
然后nut的工具显示ups.status为 OL DISCHRG,也就是ONLINE DISCHARGING,当然NUT能正常工作了。

2、查阅代码发现apcupsd只支持CAL TRIM BOOST ONLINE ONBATT OVERLOAD LOWBATT REPLACEBATT NOBATT SLAVE SLAVEDOWN 这些状态,而且是非黑即白的status,压根不支持BK650M2-CH DISCHARGING状态。而nut的status可以支持多个状态。

所以买这个的中国小伙伴注意了,Linux 下使用时 用nut-server代替 apcupsd。

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apcupsd
  • bk650m2-ch
  • problem
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore