Hi,
Here some log from my SmartUPS 1000. What do you think can cause this problem of Battery Voltage (VDC) going from 27.54 to 0,00 and the flood of alert i got ? In the console everything seem to be return at normal now.
Data log
Date
Time
Min Line Voltage
(VAC) Max Line Voltage
(VAC) Input Line Voltage
(VAC) UPS Output Voltage
(VAC) Output Frequency
(Hz) Battery Voltage
(VDC) UPS Load
(%) Internal UPS Temp
Battery Voltage (VDC)
11-07-04 10:09:26 120,2 123,1 123,1 123,1 60,00 27,40 24,7 30,6
11-07-04 09:49:27 118,0 120,9 120,9 120,9 60,00 27,40 24,7 30,1
11-07-04 09:29:27 118,0 121,6 120,9 120,9 60,00 27,40 24,7 30,1
11-07-04 09:09:27 118,8 121,6 120,9 120,9 60,00 27,54 24,7 29,7
11-07-04 08:49:27 118,0 120,9 120,9 120,9 60,25 27,54 25,3 29,7
11-07-04 08:29:27 118,8 121,6 121,6 121,6 60,00 27,54 25,3 28,8
11-07-04 08:09:34 118,0 120,9 120,9 120,9 60,25 27,54 29,2 28,3
11-07-04 07:49:49 118,8 121,6 121,6 121,6 60,00 0,00 29,9 27,4
11-07-04 06:30:40 119,5 122,4 122,4 122,4 60,00 0,00 24,7 30,6
11-07-04 06:10:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 05:50:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 05:30:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 05:10:40 120,9 123,1 123,1 123,1 60,25 0,00 24,7 30,6
11-07-04 04:50:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 04:30:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 04:10:40 120,9 123,1 123,1 123,1 60,25 0,00 24,7 30,6
11-07-04 03:50:40 120,2 123,1 123,1 123,1 60,25 0,00 24,7 30,6
11-07-04 03:30:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 03:10:40 120,2 123,1 123,1 123,1 60,25 27,40 24,7 30,6
11-07-04 02:50:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 02:30:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-04 02:10:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-04 01:50:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-04 01:30:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-04 01:10:40 120,2 123,1 123,1 123,1 60,00 0,00 27,3 31,0
11-07-04 00:50:40 120,2 123,1 123,1 123,1 60,00 0,00 27,3 31,0
11-07-04 00:30:40 120,9 123,1 123,1 123,1 60,00 0,00 27,3 30,6
11-07-04 00:10:40 120,9 123,1 123,1 123,1 60,00 27,40 24,7 30,6
11-07-03 23:50:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 23:30:40 119,5 123,1 122,4 123,1 60,00 0,00 24,7 30,6
11-07-03 23:10:40 119,5 123,1 122,4 122,4 60,00 0,00 24,7 30,6
11-07-03 22:50:40 119,5 123,1 122,4 122,4 60,00 0,00 24,7 31,0
11-07-03 22:30:40 120,2 123,1 123,1 123,1 60,25 0,00 24,7 31,0
11-07-03 22:10:40 120,2 123,1 123,1 123,1 60,25 0,00 24,7 31,0
11-07-03 21:50:40 119,5 122,4 122,4 122,4 60,25 0,00 24,7 31,0
11-07-03 21:30:40 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-03 21:10:40 118,8 122,4 121,6 121,6 60,00 0,00 24,7 31,0
11-07-03 20:50:40 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-03 20:30:40 118,8 122,4 121,6 121,6 60,00 0,00 24,7 31,0
11-07-03 20:10:40 119,5 122,4 122,4 122,4 60,25 0,00 24,7 31,0
11-07-03 19:50:40 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-03 19:30:40 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-03 19:10:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-03 18:50:40 121,6 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 18:30:40 121,6 123,8 123,8 123,8 60,00 27,40 24,7 31,0
11-07-03 18:10:40 120,9 123,8 123,1 123,1 60,00 27,40 24,7 31,0
11-07-03 17:50:40 121,6 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 17:30:40 120,9 123,8 123,1 123,1 60,00 27,40 24,7 31,0
11-07-03 17:10:40 120,9 123,1 123,1 123,1 60,00 27,40 24,7 31,0
11-07-03 16:50:40 121,6 123,8 123,8 123,8 60,00 27,40 24,7 31,0
11-07-03 16:30:40 121,6 123,8 123,8 123,8 60,00 27,40 24,7 31,0
11-07-03 16:10:40 120,9 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 15:50:40 121,6 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 15:30:40 120,9 123,8 123,1 123,1 60,00 27,40 24,7 31,0
11-07-03 15:10:40 121,6 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 14:50:40 121,6 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 14:30:40 121,6 124,5 123,8 124,5 60,00 0,00 24,7 31,0
11-07-03 14:10:40 121,6 123,8 123,8 123,8 60,00 0,00 24,7 31,0
11-07-03 13:50:40 120,9 123,8 123,1 123,1 60,00 0,00 24,7 31,0
11-07-03 13:30:40 120,9 123,8 123,1 123,1 60,00 0,00 24,7 31,0
11-07-03 13:10:40 120,9 123,8 123,1 123,8 60,00 0,00 24,7 31,0
11-07-03 12:50:40 120,9 123,8 123,8 123,1 60,00 0,00 24,7 30,6
11-07-03 12:30:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 12:10:40 120,9 123,8 123,1 123,8 60,00 0,00 24,7 30,6
11-07-03 11:50:40 118,8 121,6 121,6 121,6 60,00 0,00 24,7 30,6
11-07-03 11:30:40 118,8 122,4 121,6 121,6 60,25 0,00 24,7 31,0
11-07-03 11:10:40 119,5 122,4 122,4 122,4 60,00 27,40 24,7 31,0
11-07-03 10:50:40 118,8 121,6 121,6 121,6 60,00 27,40 24,7 31,0
11-07-03 10:30:40 118,8 122,4 121,6 122,4 60,00 27,40 24,7 31,0
11-07-03 10:10:41 118,8 121,6 121,6 121,6 60,00 0,00 24,7 30,6
11-07-03 09:50:41 120,2 123,1 123,1 123,1 60,25 0,00 24,7 30,6
11-07-03 09:30:41 118,8 121,6 121,6 121,6 60,00 0,00 24,7 30,6
11-07-03 09:10:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 30,6
11-07-03 08:50:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 30,6
11-07-03 08:30:41 119,5 122,4 122,4 122,4 60,25 0,00 24,7 30,6
11-07-03 08:10:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 30,6
11-07-03 07:50:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 07:30:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 07:10:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 06:50:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 06:30:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 06:10:40 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 05:50:40 120,9 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-03 05:30:41 120,9 123,1 123,1 123,1 60,00 27,40 24,7 31,0
11-07-03 05:10:41 120,2 123,1 123,1 123,1 60,00 27,40 24,7 31,0
11-07-03 04:50:41 120,2 123,1 123,1 123,1 60,00 27,40 24,7 30,6
11-07-03 04:30:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 04:10:41 120,2 123,1 123,1 123,1 60,25 0,00 24,7 30,6
11-07-03 03:50:41 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 03:30:41 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 03:10:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 02:50:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 02:30:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 02:10:41 120,9 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 01:50:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-03 01:30:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-03 01:10:41 120,2 123,1 123,1 123,1 60,00 0,00 27,3 31,0
11-07-03 00:50:41 120,2 123,1 123,1 123,1 60,00 27,40 27,3 31,0
11-07-03 00:30:41 120,2 123,1 123,1 123,1 60,00 27,40 27,3 30,6
11-07-03 00:10:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 30,6
11-07-02 23:50:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-02 23:30:41 119,5 123,1 123,1 123,1 60,00 0,00 24,7 30,6
11-07-02 23:10:41 120,2 123,1 123,1 123,1 60,25 0,00 24,7 31,0
11-07-02 22:50:41 119,5 123,1 122,4 122,4 60,00 0,00 24,7 31,0
11-07-02 22:30:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-02 22:10:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-02 21:50:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-02 21:30:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-02 21:10:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-02 20:50:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-02 20:30:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,0
11-07-02 20:10:41 119,5 122,4 122,4 122,4 60,00 0,00 24,7 31,0
11-07-02 19:50:41 120,2 123,1 123,1 123,1 60,00 0,00 24,7 31,5
11-07-02 19:30:41 119,5 123,1 122,4 122,4 60,00 27,40 24,7 31,5
11-07-02 19:10:41 119,5 122,4 122,4 122,4 60,00 27,40 24,7 31,5
11-07-02 18:50:41 119,5 122,4 122,4 122,4 60,25 27,40 24,7 31,5
11-07-02 18:30:41 121,6 124,5 123,8 124,5 60,00 27,40 24,7 31,5
11-07-02 18:10:41 121,6 124,5 124,5 124,5 60,00 27,40 24,7 31,5
11-07-02 17:50:41 122,4 124,5 124,5 124,5 60,00 27,40 24,7 31,0
11-07-02 17:30:41 122,4 124,5 124,5 124,5
Events
11-07-03 22:40:54 Battery Reconnected
11-07-03 22:40:39 Insufficient Runtime Available
11-07-03 22:40:35 Battery Disconnected
11-07-03 22:40:19 Sufficient Runtime Available
11-07-03 22:40:14 Battery Reconnected
11-07-03 22:29:01 Insufficient Runtime Available
11-07-03 22:28:57 Battery Disconnected
11-07-03 22:28:41 Sufficient Runtime Available
11-07-03 22:28:36 Battery Reconnected
11-07-03 22:25:48 Insufficient Runtime Available
11-07-03 22:25:44 Battery Disconnected
11-07-03 22:25:35 Sufficient Runtime Available
11-07-03 22:25:30 Battery Reconnected
11-07-03 22:24:46 Insufficient Runtime Available
11-07-03 22:24:42 Battery Disconnected
11-07-03 22:24:25 Sufficient Runtime Available
11-07-03 22:24:21 Battery Reconnected
11-07-03 22:23:54 Insufficient Runtime Available
11-07-03 22:23:50 Battery Disconnected
11-07-03 22:23:34 Sufficient Runtime Available
11-07-03 22:23:29 Battery Reconnected
11-07-03 22:17:17 Insufficient Runtime Available
11-07-03 22:17:13 Battery Disconnected
11-07-03 22:17:04 Sufficient Runtime Available
11-07-03 22:16:59 Battery Reconnected
11-07-03 22:01:44 Insufficient Runtime Available
11-07-03 22:01:39 Battery Disconnected
11-07-03 22:01:23 Sufficient Runtime Available
11-07-03 22:01:19 Battery Reconnected
11-07-03 22:01:05 Insufficient Runtime Available
11-07-03 22:01:01 Battery Disconnected
11-07-03 22:00:51 Sufficient Runtime Available
11-07-03 22:00:47 Battery Reconnected
11-07-03 22:00:01 Insufficient Runtime Available
11-07-03 21:59:57 Battery Disconnected
11-07-03 21:59:41 Sufficient Runtime Available
11-07-03 21:59:36 Battery Reconnected
11-07-03 21:59:10 Insufficient Runtime Available
11-07-03 21:59:06 Battery Disconnected
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:54 PM . Last Modified: 2024-03-20 03:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:54 PM . Last Modified: 2024-03-20 03:41 AM
Ok, thanks
We gonna do a little maintenance on it and if the problem appear again, i will change it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:54 PM . Last Modified: 2024-03-20 03:41 AM
Good day Eric,
Does the UPS emits a tone/beep pattern? Are there any solid or flashing LEDs infront of it? The event logs shows the battery being disconnected/reconnected frequently and I assume that you are not doing it physically. Let see if it would stop/change once we reseated the battery connector.
Have you ever replace the battery on this unit? Can you also provide the model and serial number of the UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:54 PM . Last Modified: 2024-03-20 03:41 AM
If the UPS would show a flashing replace battery icon physically it could only mean one thing, the UPS is telling us that there is a disconnected battery condition. Most of the time, the failure/fault is not on the battery but on the UPS itself.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:54 PM . Last Modified: 2024-03-20 03:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:54 PM . Last Modified: 2024-03-20 03:41 AM
Ok, thanks
We gonna do a little maintenance on it and if the problem appear again, i will change it.