Voltage Regulation - Line-R versus APC AV versus UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Voltage Regulation - Line-R versus APC AV versus UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:53 PM . Last Modified: ‎2024-03-20 03:41 AM

0 Likes
2
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:53 PM . Last Modified: ‎2024-03-20 03:41 AM

Voltage Regulation - Line-R versus APC AV versus UPS

Hello all! I'm a bit confused on the subject of voltage regulation, and what each product does about it.

Right now, I have a BackUPS XS 1500, which has a sensitivity setting (Low, Medium, or High, currently set to High since it doesn't click over to battery very often) and an acceptable voltage range (currently set between 88 and 136 volts). Is there circuitry in the UPS that irons out anomalies in line power, or is it only capable of switching between battery and line, choosing battery when line power seems faulty (or missing)? What relationship does the sensitivity setting have to the acceptable voltage range - does the battery only kick in if line voltage is outside of that range, or does sensitivity refer to a different kind of line anomaly?

Does the Line-R product merely do the same as the UPS, using something else in lieu of a battery (but of course providing no help in the event of a power loss)? How does its functionality differ from the APC AV line conditioner products?

Any info would be greatly appreciated. Thanks!

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:53 PM . Last Modified: ‎2024-03-20 03:41 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:53 PM . Last Modified: ‎2024-03-20 03:41 AM

Hi Rask,

Good questions.

The [Line-R|http://www.apcmedia.com/salestools/ASTE-6Z7V37_R0_EN.pdf] can boost the input voltage up to 5% or trim it down to -12% to keep the output voltage within an acceptable range. If it cannot keep the output voltage within the acceptable range, it cuts off the output.

The [BackUPS XS 1500|http://www.apcmedia.com/salestools/ASTE-6Z7V26_R0_EN.pdf] can boost the input voltage up to 5% to keep the output voltage within an acceptable range. If it cannot keep the output voltage within the acceptable range, it remains on battery. If the battery becomes depleted, the output shuts off.

Both also have filters that protect against voltage spikes and surges.

>
What relationship does the sensitivity setting have to the acceptable voltage range - does the battery only kick in if line voltage is outside of that range, or does sensitivity refer to a different kind of line anomaly?
>

Very observant--acceptable output voltage range and sensitivity are not directly related, although the sensitivity button on the back of the UPS will change both at the same time (details in the manual). Exceeding either threshold will cause the UPS to go on battery or stay on battery.

Line voltage is an average (well, RMS) voltage over a line cycle, while sensitivity looks at the instantaneous voltage compared with the expected AC waveform. Typically a change in voltage will first appear as a distortion of the expected AC waveform. The UPS detects the distortion (anticipating a problem), transfers to battery, and waits for a clean, undistorted AC waveform. When the input power is clean, the line voltage determines whether it goes back online, boosts, trims, or remains on battery.

>
How does its functionality differ from the APC AV line conditioner products?
>

The Line-R and the BackUPS are designed to protect equipment from power problems, but do little to clean up distortions in the AC waveform, or noise. We don't worry about this because most consumer electronics simply doesn't care. The BackUPS does detect distortions (sensitivity), but only for the purpose of anticipating power problems.

Some people do care about getting a clean AC waveform. The AV product line includes additional line filtering to remove noise on the line. The AV UPS produces a clean sine wave while on battery.

So to summarize:

Line-R:
- Automatic voltage regulation
- Surge protection
BackUPS
- (some) Automatic voltage regulation
- Surge protection
- Battery for when line is bad
- Produces stepped-approximated sine wave on battery
SmartUPS
- Automatic voltage regulation
- Surge protection
- Battery for when line is bad
- Produces clean sine wave while on battery
AV UPS
- Automatic voltage regulation
- Surge protection
- Battery for when line is bad
- Produces clean sine wave while on battery
- Contains additional line filtering to remove noise when not on battery

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:53 PM . Last Modified: ‎2024-03-20 03:41 AM

0 Likes
0
2239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:53 PM . Last Modified: ‎2024-03-20 03:41 AM

Hi Rask,

Good questions.

The [Line-R|http://www.apcmedia.com/salestools/ASTE-6Z7V37_R0_EN.pdf] can boost the input voltage up to 5% or trim it down to -12% to keep the output voltage within an acceptable range. If it cannot keep the output voltage within the acceptable range, it cuts off the output.

The [BackUPS XS 1500|http://www.apcmedia.com/salestools/ASTE-6Z7V26_R0_EN.pdf] can boost the input voltage up to 5% to keep the output voltage within an acceptable range. If it cannot keep the output voltage within the acceptable range, it remains on battery. If the battery becomes depleted, the output shuts off.

Both also have filters that protect against voltage spikes and surges.

>
What relationship does the sensitivity setting have to the acceptable voltage range - does the battery only kick in if line voltage is outside of that range, or does sensitivity refer to a different kind of line anomaly?
>

Very observant--acceptable output voltage range and sensitivity are not directly related, although the sensitivity button on the back of the UPS will change both at the same time (details in the manual). Exceeding either threshold will cause the UPS to go on battery or stay on battery.

Line voltage is an average (well, RMS) voltage over a line cycle, while sensitivity looks at the instantaneous voltage compared with the expected AC waveform. Typically a change in voltage will first appear as a distortion of the expected AC waveform. The UPS detects the distortion (anticipating a problem), transfers to battery, and waits for a clean, undistorted AC waveform. When the input power is clean, the line voltage determines whether it goes back online, boosts, trims, or remains on battery.

>
How does its functionality differ from the APC AV line conditioner products?
>

The Line-R and the BackUPS are designed to protect equipment from power problems, but do little to clean up distortions in the AC waveform, or noise. We don't worry about this because most consumer electronics simply doesn't care. The BackUPS does detect distortions (sensitivity), but only for the purpose of anticipating power problems.

Some people do care about getting a clean AC waveform. The AV product line includes additional line filtering to remove noise on the line. The AV UPS produces a clean sine wave while on battery.

So to summarize:

Line-R:
- Automatic voltage regulation
- Surge protection
BackUPS
- (some) Automatic voltage regulation
- Surge protection
- Battery for when line is bad
- Produces stepped-approximated sine wave on battery
SmartUPS
- Automatic voltage regulation
- Surge protection
- Battery for when line is bad
- Produces clean sine wave while on battery
AV UPS
- Automatic voltage regulation
- Surge protection
- Battery for when line is bad
- Produces clean sine wave while on battery
- Contains additional line filtering to remove noise when not on battery

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:54 PM . Last Modified: ‎2024-03-20 03:41 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:54 PM . Last Modified: ‎2024-03-20 03:41 AM

Thanks very much for a highly informative response!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore