Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Posted: 2021-09-01 04:33 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-01 04:33 AM
Hi
I have a BackUPS CS-500. Status (On Line) light is Green; there are no warning lights.
The UPS is connected via USB to my NAS. The UPS supplies power to the NAS and to a Mac Mini.
Via the software on the NAS, I can see that the UPS battery is fully charged; and that the load on the UPS is around 40%. However, estimated runtime is reported as zero. (I have checked these numbers via the network as well using some separate third-party software. Note that I do not have access to a Windows machine, so I cannot run 'powerchute'.)
Based on the power curve, I would expect the UPS to be able to power the NAS and the Mac for ~10 minutes. However, when a power outage occurs, as it did this morning, the UPS switches off entirely within about 30 seconds... just about long enough for the NAS to report a switch to battery mode.
The UPS was purchased new in July 2019; the battery has never been replace (so there are no third-party battery issues at play). As noted earlier, the status lights on the UPS are all clear.
It's evident that the behaviour during a power outage, and the reported 'zero' runtime, are not correct. Does anyone have any thoughts about how to troubleshoot?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-01 01:04 PM
@Anonymous user
If the UPS shows zero runtime, that indicates the battery/batteries are degraded and cannot sustain the load, even when reporting charged fully. The same as an automotive battery. It can be fully charged, but once you attempt to start the vehicle, a load is applied the charge drops rapidly.
I suggest pulling the battery once charged and checking the voltage. A good battery should read 13.6v DC.