Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-ups & Smart-ups failing during power flickers

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-ups & Smart-ups failing during power flickers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

0 Likes
3
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

Back-ups & Smart-ups failing during power flickers

I have two Back-ups 500's and a Smart-ups 1500 that must be at least 15 years old. I typically cycle the batteries every 3-4 years and they've worked no worries for all this time. But recently I notice they don't transfer power during grid flickers and my computers shut down. However, should I throw the panel breaker, they will kick on.

Is my UPS hardware just getting long in the tooth or could there be another issue? None of them have the computers directly hooked up to them (there is either extension cords or power strips in line).

Thanks in advance for the advice.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

0 Likes
0
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

Thanks for the reply Matt,

I'm using the SUA1500 & a Back-UPS500.  One of the 500's does not have the issue, but the other as well as the 1500 do. The UPS fail only began in the last year. Before that all functioned well when there were flickers.

I can sure try your suggestion on the 1500 but that still leaves the 500 that fails. Is this kind of thing a normal problem with an aged UPS?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

0 Likes
1
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

Hi David 

One thing it may be causing this during power flickers is the transfer time.

If the power flickers off and back on, the 8-10ms transfer time (for a back UPS) or 6-8ms (for a SUA on medium sensitivity) will double as it is switching twice once to battery and then straight back to online. Whereas when you flick the breaker it is only switching to battery.

You could try altering the sensitivity setting on your UPS to see if this helps.

 

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

0 Likes
0
1865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:02 AM . Last Modified: ‎2024-03-26 03:44 AM

Thanks for the reply Matt,

I'm using the SUA1500 & a Back-UPS500.  One of the 500's does not have the issue, but the other as well as the 1500 do. The UPS fail only began in the last year. Before that all functioned well when there were flickers.

I can sure try your suggestion on the 1500 but that still leaves the 500 that fails. Is this kind of thing a normal problem with an aged UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

kaltal
kaltal
Explorer

Posted: ‎2024-09-26 11:07 AM

In response to BillP
0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 11:07 AM

Hello,

I have the same problem.  Quick power flickers cause the UPS to go into fault/alarm and cuts off power to anything connected to it.  Clean power outage doesn't cause any issues, and the UPS continues powering the units for a good while.  Unfortunately, my UPS doesn't have a sensitivity adjustment.  It is UPS 1500 model BN1500M2. Any possible solutions for that?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore