Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Back-UPS XS 1300 does not "see" battery connected

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Back-UPS XS 1300 does not "see" battery connected
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:15 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
14
3703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:15 AM . Last Modified: ‎2024-03-22 12:00 AM

Back-UPS XS 1300 does not "see" battery connected

I have four APC Back-UPS XS LCD units. Two are model 1300 and two are 1500.

The 1300 units have been on continuously for nearly two years with never a problem. Now, one of the units can no longer detect the battery as connected. I removed the battery and checked the voltage with a DMM and it shows 26 VDC. Nevertheless, when I re-connect the battery and turn the unit on, the LED battery symbol is empty of bars and blinks while the unit emits a chirp-chirp sound every second. This is the same symptom if the battery is disconnected.

Any recommendations on things to check? I'm an electronics major and would like to check the simple stuff before I chuck it in the trash. I paid around $100 for this thing brand new, and it simply isn't worth the money to ship this heavy thing back and forth.

Thanks!
Mike

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

Hi Mike.

Since you have mentioned that you have two (2) 1300's
and only one of them shows the flashing battery icon, you can remove the
battery from the working unit and put it on the unit that is chirping
or shows the flashing battery icon. If the condition clears, you can
replace the batteries. Also, the BackUPS units that you have is covered
with a 3 year warranty on it. Can you send me the serial numbers and model numbers of your UPS's thru PM along with your contact details?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

My XS1300 was fine until I removed the battery because we were moving and I didn't know how long it would be in storage not connected to AC power.

I reconnected the battery and it's just flashing, not charging. When I plug something into the back, it shows the load.

8B0823R27183

My other four APC UPS units are working fine after being reconnected.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

We only recommend buying our RBC's. Although I'm sure it's possible to replace one of the two batteries, we don't recommend doing that for a few reasons. First of all, there are dozens of options for batteries of this size out there and the one you buy may not be the correct size,specs etc. We don't make these batteries directly so we only sell batteries for our units. So if a UPS requires two batteries connected in series, we only sell those two batteries together. Also, connecting a brand new battery to an older battery is likely not a good idea as well. At the very least, it will not give you a 100 % accurate runtime although that's not to say it will not work.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 14
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

Hi Mike.

Since you have mentioned that you have two (2) 1300's
and only one of them shows the flashing battery icon, you can remove the
battery from the working unit and put it on the unit that is chirping
or shows the flashing battery icon. If the condition clears, you can
replace the batteries. Also, the BackUPS units that you have is covered
with a 3 year warranty on it. Can you send me the serial numbers and model numbers of your UPS's thru PM along with your contact details?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

My XS1300 was fine until I removed the battery because we were moving and I didn't know how long it would be in storage not connected to AC power.

I reconnected the battery and it's just flashing, not charging. When I plug something into the back, it shows the load.

8B0823R27183

My other four APC UPS units are working fine after being reconnected.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

Hi Erik,

Are the working UPSes of the same model? If they are, can you try using the working battery on the UPS that shows the problem? If the replace battery LED is flashing it means that the UPS is not detecting the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

JonPro Said: "I would suggest that you order the battery that comes with your BackUPS 1300."

I did - pulling of the APC sticker revealed: "Vision CP 1290" - nothing special about that.

Less than $20 versus $80 from APC.

It's working great.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

I don't have another one of the same model, but I tested the voltage of their batteries and the ES-650's one battery is close to the same voltage as one of the XS-1300 batteries.

Each of the two batteries in my XS-1300 show 27.5 volts
The battery in the ES-650 is 26.6 volts.

I connected each of the batteries from the 1300 into the 650, one of them triggered the battery fault.

I then connected the good battery from the 1300 bundle with the battery from the 650, connected them to the 1300 and all is good.

So I just need to order a single replacement battery for my 1300. I only see them being sold a pairs. Any way round this or just order a battery for the ES-650?

Message was edited by: hacker-pschorr

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

I would suggest that you order the battery that comes with your BackUPS 1300.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

I would love to, but as I already explained this unit has a double battery setup and only one of the batteries is bad:

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=APCRBC109

Why spend twice the money and toss out a perfectly good battery????

I guarntee you APC uses the single battery in something, and I would like to purchase that unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

Ok you cant mix old and new YOU JUST SIMPLY CANT! (i dont have time to explain...)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

We only recommend buying our RBC's. Although I'm sure it's possible to replace one of the two batteries, we don't recommend doing that for a few reasons. First of all, there are dozens of options for batteries of this size out there and the one you buy may not be the correct size,specs etc. We don't make these batteries directly so we only sell batteries for our units. So if a UPS requires two batteries connected in series, we only sell those two batteries together. Also, connecting a brand new battery to an older battery is likely not a good idea as well. At the very least, it will not give you a 100 % accurate runtime although that's not to say it will not work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

Most manufacturers recommend that you only buy replacement parts from them. They also charge considerably more than do aftermarket parts. I'd like more substantial reasons to plonk down the extra cash than physical dimensions or being able to choose a 9.0 Ah battery over a 7.0 Ah one. Yes, you get what you pay for - sometimes.

Like many others on these fora, my UPS just started blinking an empty battery. Like many others I don't want to drop $50 on new batteries in the hope that it will fix the problem. The batteries in series measure 26.25 VDC - I will try the 12V bulb test tomorrow and I will check each cell individually. The power leads to the battery measured 27.6 VDC. Is there a way for the average user to determine if the charging circuit is working properly?

Message was edited by: Fenris

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-22 12:00 AM

I have the exact same issue, except when mine failed it just turned off completely. I turned it back on and get the exact same thing as the original poster. Mine are about 2 years old as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-21 11:59 PM

0 Likes
0
3701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-21 11:59 PM

Hi Chuck,

Can you provide the exact model number of the UPS? And can you also tell us the exact scenario that is going on with your unit? Does it support the load when it goes on battery? What kind of beep, LED or LCD patterns are you seeing on your unit?

You have mentioned that the unit turns off completely, does it do it while it is online or when it transferred to battery? Do you have any APC software installed on the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-21 11:59 PM

0 Likes
0
3700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-21 11:59 PM

I found that one of the two 12 volt Gel Cells in the battery pack was bad. Oddly, both batteries show the proper voltage (13.1VDC) on my DVM, but when a 12VDC auto spotlight is hooked up to each, only one of them will light the bulb.

I've heard the Gel Cell batteries can become "cooked" by a faulty charging circuit. So, I'm wondering if it makes sense to invest in replacement batteries and, if so, if it's advisable to replace both cells, or just the faulty one?

I would hate to invest $50 in two replacement gel cells, only to find out the UPS has a bad charging circuit and cook another battery. Any advice?

Message was edited by: mikebo

Message was edited by: mikebo

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-21 11:59 PM

0 Likes
0
3700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:16 AM . Last Modified: ‎2024-03-21 11:59 PM

An advice that I can give you is swapping the batteries or getting a known working battery and give it a day or two to see if it would cause any problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of