Back-UPS RS 1000 beeping continuously

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS RS 1000 beeping continuously
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

0 Likes
3
22725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

Back-UPS RS 1000 beeping continuously

Hello, this afternoon my Back-UPS RS 1000 started beeping non-stop.  It is not a continuous tone, it beeps about once per second and never stops.

- The green "On Line" LED is lit.

- The red "Replace Battery" LED is flashing.

According to the product manual, this combination of constant beeping and flashing lights indicates that the batteries are disconnected.  However, the battery is in fact installed and connected.  I tried unplugging and replugging the battery pack and nothing changed.

If I was convinced that the problem is that I need a new battery, I have no problem ordering one, but I want to confirm that a replacement battery would actually fix the problem.  It seems more like an internal battery wiring connection has failed.  In the past when I needed a new battery (on a different APC UPS) it beeped periodically for a few seconds at a time, not continuously like this.

Can anyone provide guidance on how to resolve this?

Thank you,

Dominic

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

0 Likes
0
22712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

Thank you very much for your reply Secret Squirrel!  I have turned off the UPS (and moved my loads over to a regular surge protector) for the night and I'll see what happens with it tomorrow.  Just for more information in case it is helpful, I did measure the battery voltage at the plug and it was 24.95 V. This was with the battery removed from the UPS so obviously there was no load on it.

Thanks again,

Dominic

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

0 Likes
0
22712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

Hi Dominic,

The UPS monitors the DC voltage present on it's internal DC Bus. If this voltage drops below the threshold for "detection" the UPS will think there is no battery installed even if it is. This can happen with older batteries as their ability to store DC power diminishes. I would advise disconnecting your load, turn the UPS off and leave it plugged in to utility overnight. If when you start the unit in the morning it fails to detect the battery, I would suggest a replacement of the battery or the complete unit depending upon the unit's age.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

0 Likes
0
22713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

Thank you very much for your reply Secret Squirrel!  I have turned off the UPS (and moved my loads over to a regular surge protector) for the night and I'll see what happens with it tomorrow.  Just for more information in case it is helpful, I did measure the battery voltage at the plug and it was 24.95 V. This was with the battery removed from the UPS so obviously there was no load on it.

Thanks again,

Dominic

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

0 Likes
0
22712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:43 AM . Last Modified: ‎2024-03-27 12:45 AM

After leaving the UPS to charge all night while powered off, I turned it on this morning with no loads connected.  This time it ran through the self diagnostic and the battery failed, resulting in beeping for about 1 minute and the red "Replace Battery" light on solid, not flashing.  That result is consistent with needing a new battery, so I will go ahead and purchase new batteries.  I'm still not sure why it initially failed yesterday by beeping continuously as if the battery was disconnected, but I really appreciate your suggestion Secret Squirrel so that I can feel more comfortable that new batteries will solve the problem.

Thanks again!

Dominic

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore