Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Back UPS Pro 650 Problem

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Back UPS Pro 650 Problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

0 Likes
6
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

Back UPS Pro 650 Problem

Hi,

I have had this UPS for about 8-9 years now. I have had no problems with it, and I only had to replace the battery once about 3 years ago. Now every time there's a severe brownout or blackout (very rare), the UPS tries to switch to battery power. And when that happens, the UPS cuts the power from the PC and a continuous sound signal is emitted, and the red "overloaded" lamp turns on.

I tried unplugging everything, tried a different wall outlet (who knows?), to no avail. What I don't understand is why would the "overloaded" lamp turn on only when battery power is needed?

Any help is appreciated.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 650
  • apc
  • back_ups_pro
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:18 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:18 AM

The Trade up is not available here, I just checked.

Thank you for the help. When I came here I thought it's just a forum, didn't know it's the official APC forum. Great support, customers don't forget that. ๐Ÿ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

Glottis,

Just to clarify...it sounds like the UPS is emitting a single, constant tone with the overload LED on when the unit transfers to battery, and it does this with no load at all (you said everything was unplugged during your test)? Is the overload LED blinking or solid? Are there any other LEDs on in addition to the overload LED?

Also, what is/was your load attached to the UPS?

Please advise, as this could be an indication of an internal fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

Thanks for replying, Erasmus.

Yes the UPS emits a single, constant tone with the overload LED on when the unit transfers to battery. It does that with no load at all. The overload LED is solid. None of the other LEDs are on.

The load is a single PC (Athlon64 3200+, ATI Radeon x1900xt, one 500GB hdd), with the monitor plugged in the "surge protection only" outlet.

I just found an APC Back-UPS Pro manual online which states the following: "The UPS tests
for overloads when operating on-battery and when performing self-tests"

When I initiate a self-test, the same thing happens as above. The Replace Battery LED is off all the time, so I don't think it's because of the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:58 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

This seems to be an internal UPS fault then. I would recommend trading-UP the UPS at our website (www.apc.com) or by calling our sales department (1-800-800-4272). This will give you a small discount on a new UPS, which is what I would recommend shooting for. The current sensor on the UPS could be faulty or there could be a general logic/board fault within the UPS, and there is no way to fix the issue unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:19 AM

Bad news of course, but at least now I know (approximately) what's wrong.
As for trading up, I guess I'm out of luck if I live in Eastern Europe?

I think I'm going to buy a Back-UPS ES 700VA. I already have one (another PC) and it's good enough for home PCs.

Thanks for your time Erasmus.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:18 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:18 AM

I would check the APC page for your country (drop down at top of website) to determine trade-UPS options. We do have a large division for Europe so I don't think you'll be out of luck.

No problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:18 AM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 11:59 PM . Last Modified: โ€Ž2024-03-22 04:18 AM

The Trade up is not available here, I just checked.

Thank you for the help. When I came here I thought it's just a forum, didn't know it's the official APC forum. Great support, customers don't forget that. ๐Ÿ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of