Back-UPS LS 700 chirps every 3 min with Replace Battery light

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS LS 700 chirps every 3 min with Replace Battery light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-22 04:21 AM

0 Likes
6
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-22 04:21 AM

Back-UPS LS 700 chirps every 3 min with Replace Battery light

Hi all. I have a Back-UPS LS 700, sn NB0204252200, which recently started chirping and flashing the Replace Battery light--It does a double chirp with the flashing light, a few seconds later it does the double chirp again; repeated every few minutes, never less than 3 minutes, sometimes longer.

I assumed this meant the battery needed replacing, so I bought a new APC battery from Amazon, installed it, and it's still doing the chirp thing. I am hoping that this is a temporary situation and will go away when the battery gets charged up, but from other threads on this forum I wonder if there is something wrong with the UPS instead. A multimeter measures the old battery at 13 volts.

There are only some network switches and a phone system plugged into this unit, no software, no USB, no computer. It worked fine for years; the battery I removed was a replacement (I know because it's an ABC, not an APC) but I can't remember how long it was in there. I have tried sliding the new batter out halfway and making sure the plugs are pushed on all the way. When I installed the new battery and turned the unit back on, it passed the self test.

I see from the docs that a manual self test should be performed after the battery is fully charged, so I will do one tomorrow.

It would be nice to find out if I should just buy a new UPS. This is a newspaper and most of our phone system is plugged into this unit, so it's pretty important that it be reliable. Any suggestions?

Thanks

--Colleen

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

This random "Battery Disconnect" error seems to be a common problem with these Back-UPS LS700's. I have at least 8 of these units with the same exact problem, the red light comes on, they chirp, and the power management software says that the battery is disconnected. Then it 'reconnects' for a little while, then the same error and beeps again. We are using official APC RBC-17 batteries shipped directly from APC, so the batteries are NOT the problem.

All are Model: BPC700UC
I have been using APC UPS's for many may years and this is the only model that I have encountered that has this issue. APC should recall this model since they ALL seem to have the same problem...

We've already recycled a bunch of them and here are a few of the SN's from the ones that we still have:

3B053939X24704
4B0515P58272
4B0515P58269
NB0204251511

Is it a coincidence that all of these BPC700UC units are failing the same exact way? I think not...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-22 04:21 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:56 PM . Last Modified: ‎2024-03-22 04:21 AM

I have a Back-UPS 700 that is doing the same thing. Did you replace yours? I am trying to decide whether to replace the battery. I will probably just trade it in with some other old ones that I have, but was curious as to what you did. I have never had one behave this way. I am also having trouble getting the UPS turned off, so it may be faulty.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:21 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:21 AM

Ann,

As far as I know, the purpose of the "Flashing Replace Battery LED" is to indicate that the Battery is not connected to the UPS. If the Battery is connected to the UPS firmly, the FRBL should not lit.

In this situation, I would not replace the battery. So My advice for you is that please replace the unit to a new unit.

Have a great day!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

hi colleen,

sometimes if there is a problem with the UPS circuitry, this issue can occur. the best solution is to do a UPS self test as you already came up with to see if it clears the replace battery LED. the other option would just to simulate a power outage by pulling the plug from the wall on the UPS to see if it supports a load. keep in mind that if for some reason, if the unit has a problem transferring to battery, this may drop the load so maybe you want to do this with a non critical load.

if the UPS passes the self test/pull plug test, it would be a cosmetic issue most likely where the replace battery LED is flashing but the unit still can use its battery and wouldnt necessarily require a replacement unless you couldnt stand the replace battery LED flashing - the only problem would be in the future for a replacement battery, the LED wouldnt work correctly.

if the self test/pull plug test drops the load, then there is something else going on where the UPS cannot see the battery at all and I think a replacement would be best.

overall, with the unit's age, you could think about the APC Trade UPS program and get a discount towards a new UPS which comes with a three year warranty and new battery of course.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

OK, I'll try the load test in a few days (I can't unplug the phone system and half the network before then!) Assuming the unit performs ok...

1. "the only problem would be in the future for a replacement battery, the LED wouldnt work correctly." So, evidently the normal replace-battery warning of the light being steady-on won't work when it's stuck in this chirping mode?

2. If I decide to at least let my two good batteries wear out first (I'd have to swap them every few months), is there any way to shut up the chirping? The light we can live with. The chirping annoys people.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

1.) to be honest, i'd have to test it but i am leaning towards the LED will always be flashing and will not be able to stay solid when the battery needs to be replaced next.

2.) i believe you can install powerchute personal to attempt to mute all alarms. i vaguely remember hearing that the only alarm you cannot disable is the replace battery alarm though - because of the fact that its trying to warn you that you need to replace it or the UPS wouldnt work - BUT i think i have spoken to someone who has done it. so i think its worth a try. within powerchute personal edition, you want to go under Configuration->Notification.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

0 Likes
0
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:57 PM . Last Modified: ‎2024-03-22 04:20 AM

This random "Battery Disconnect" error seems to be a common problem with these Back-UPS LS700's. I have at least 8 of these units with the same exact problem, the red light comes on, they chirp, and the power management software says that the battery is disconnected. Then it 'reconnects' for a little while, then the same error and beeps again. We are using official APC RBC-17 batteries shipped directly from APC, so the batteries are NOT the problem.

All are Model: BPC700UC
I have been using APC UPS's for many may years and this is the only model that I have encountered that has this issue. APC should recall this model since they ALL seem to have the same problem...

We've already recycled a bunch of them and here are a few of the SN's from the ones that we still have:

3B053939X24704
4B0515P58272
4B0515P58269
NB0204251511

Is it a coincidence that all of these BPC700UC units are failing the same exact way? I think not...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore