Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back UPS CS 500VA old?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS CS 500VA old?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

0 Likes
2
1237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

Back UPS CS 500VA old?

I have this UPS almost 6 years (last year bought new battery) so far so good, but the problem started few months ago...
Some months back i noticed sometimes it lose the USB connetction with PC (native control panel) and after some time it come back (tested Vista and XP dual boot) but thats not so big problem

Today it gone mad while there was fine power current input it just stared verryyyy fast switching on/off from battery to input current (10 times per secand), shuting down did not help, after battery test again it started, than i tried to unplag it from power for 20-30 secands (and hear that beep like curent being let out from capacitor) and it started to work again

I think something inside is failling being quite old, i have friend electrician he could take a look..., any advice what might went wrong?

I also notice in last week once it didn`t manage to respond on short (less than a secand power loss) thats the first time it failed me becouse here we have lots of those short power cuts (Sebia is gr8 country for campany like APC 😛 )...

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

0 Likes
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

the battery is replaced 1.5 years ago with Haze HZS 12V 12Ah, its not original becouse here it was a bit hard to find same type.., and it has more Ah (original has 7.2Ah) but so far that was not a problem
PC and TFT is on a battery output
i know about changing sensitive mode, first thing i did that with no help, it was on medium now is on low sensitive mode
every few days i have few short power cuts and it works fine and holds PC + TFT ~10 minuts

today fast switching was really iregular like i sad very fast, looked like 10-15 swiches in 1sec, i know it can be from inproper input but i sow that many times in past and this did not look like that, also ups refused to switch on normaly (its still was on fast swiching mood) i tried many turn off/on changing sensitive mode ect.. till i disconneted and waited for it to discharge from main power only after that it resumed work

also while it was on fast switch mode i tried cuting power from it so hoping it would stay on battery that also didn`t help, it just restarted mine PC

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

0 Likes
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

When Back-UPS like these rapidly switch to and from battery mode, it's very often in response to an input power problem such a line distortion or total harmonic distortion (THD).

Your UPS can be commanded to be less sensitive to these small variances in input power quality. This would result in the UPS not using its battery when the power quality is reduced, which can happen naturally in response to many environmental or power grid issues.

To manually adjust your UPS' sensitivity:

-power down your attached equipment
-turn off the UPS with the power button
-with the UPS still connected to good AC power, press and hold the power button for approximately 10 seconds.
-when you see all the LEDs on the front of the UPS flash together, release the power button.
-repeatedly press the power button to cycle through the different settings. (3 LEDs ON = High Sensitivity, 2 LEDs ON = Medium, 1 LED ON = Low)
-when the UPS is flashing either 1 or 2 LEDs, wait for the UPS to turn off and save the new parameters.

Now just power on your UPS normally by briefly pressing that same power button. The UPS should now be using the new medium or low sensitivity, depending on how many LEDs were flashing when you changed the setting with the procedure above.

Now, as far as the problem you had where you noticed the UPS fail to keep your equipment running during a very short outage, were the devices that were powered down connected to the Battery Backup outlets on the back of the UPS? Keep in mind that one column of outlets, designated "surge protection only", will not provide any battery power during even short outages. Only the outlets marked "battery back-up" provide battery power through outages.

You also mentioned the UPS is 5 years old. It may be time to replace your battery. Given most batteries have a useful life of 3-5 years, depending on usage and environment, I would say your UPS is due for a new battery. This is an easy procedure to change the battery. The part for the battery kit for your Back-UPS CS 350 is RBC2.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:27 PM . Last Modified: ‎2024-03-26 12:26 AM

the battery is replaced 1.5 years ago with Haze HZS 12V 12Ah, its not original becouse here it was a bit hard to find same type.., and it has more Ah (original has 7.2Ah) but so far that was not a problem
PC and TFT is on a battery output
i know about changing sensitive mode, first thing i did that with no help, it was on medium now is on low sensitive mode
every few days i have few short power cuts and it works fine and holds PC + TFT ~10 minuts

today fast switching was really iregular like i sad very fast, looked like 10-15 swiches in 1sec, i know it can be from inproper input but i sow that many times in past and this did not look like that, also ups refused to switch on normaly (its still was on fast swiching mood) i tried many turn off/on changing sensitive mode ect.. till i disconneted and waited for it to discharge from main power only after that it resumed work

also while it was on fast switch mode i tried cuting power from it so hoping it would stay on battery that also didn`t help, it just restarted mine PC

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore