Back UPS BN1500M2: Powerchute reports batery charging and at 97%, for 2 days!

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS BN1500M2: Powerchute reports batery charging and at 97%, for 2 days!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:49 PM . Last Modified: ‎2024-03-26 02:53 AM

0 Likes
1
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:49 PM . Last Modified: ‎2024-03-26 02:53 AM

Back UPS BN1500M2: Powerchute reports batery charging and at 97%, for 2 days!

So, my old BX 1500G that I had already replaced the battery in once in the

nearly 11 years I've owned it failed the other night, with a bad/faulty battery warning.

Decided to just buy a new APC UPS this time, since the unit was almost 11 years old now.

Checked on-line at my local Best Buy and picked up a new APC  BN1500M2.

The unit plugged right into the same data cable that my old one used, I see no real difference

in the new cable and the old cable and since the USB port on my PC where the data cable is plugged in is

somewhat difficult to get to I just used the old cable.

Powerchute picked up the new UPS just fine (still had the software installed from the old unit) and

although Powerchute kept periodically prompting me to upgrade to the newer version (3.1.0) I never

really bothered. Everything seemed to be fine, never had any problems.

 

So, in powerchute I ran a manual self-test of the new UPS, passed the test. Looked into the settings

and adjusted the sensitivities and voltage settings as I had them set before with the older UPS.

Just to verify the unit was OK, I turned off the power strip the unit was plugged into while under the load

of my PC and monitor to simulate an actual power failure.

 

Unit worked just fine. Did notice the charge level of the battery was down a bit, I let it run on battery for

around 15 to 20 seconds. If I remember correctly, it was only down to around 95 percent or thereabouts.

 

Now, 24 hours later, still saying charge is only at 97%. I had my PC shut down over night, around 8 to 10 hours,

and I leave my UPS ON all the time, never shut the UPS off. I thought maybe it was time to upgrade powerchute

software to version 3.1.0 So I upgraded to the new version, see if it made a difference. No Change.

Shouldn't it be showing more than 97% charge? I've had no significant power problems over night (the

clock on the microwave would have definitely been off by several hours).

 

Did another manual self test, using the power chute software. Passed the test, then battery charge level dropped from 97%

down to 96%. About 30 minutes later was back up to 97% and has been there every since. That was about 2 hours

ago and it has remained at 97%.

 

Is 97% the "new 100%" or something?

I've tried un-installing powerchute from within the windows 10 Programs and Features, then re-booted PC,

then re-installed Powerchute.

Same result: Battery charge level is stuck at 97% and is not going up.

Anyone run into this before? Even my even older (probably 15 years ago) 900va APC unit never had this issue.

If there was a power problem, my APC's worked fine, then the battery level would slowly climb back up to

100% within a short time, maybe a couple hours at most.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:49 PM . Last Modified: ‎2024-03-26 02:53 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:49 PM . Last Modified: ‎2024-03-26 02:53 AM

So, just an update:

Day 3 now of having the new UPS, and it is FINALLY showing 100% charge.

According to the specs in the owner's manual, the battery should FULLY CHARGE in 16 hours.

I have a 30 day return window at Best Buy, and am really curious if this seems normal.

Granted, over the 11 years I have owned my BX 1500G I never really paid too close attention

to the charge level, but 2 to 3 days seems a bit excessive for a brand new UPS to fully charge,

especially when the charge level STARTED at around 97%.

I'd consider ordering a new battery cartridge for my BX 1500G, but 2 things:

1) The unit is 11 years old and well past it's warranty

2) I immediately pulled the battery out at the first sign of trouble and checked it with

a volt meter, and was getting around 26.5vdc so to me, that seems about right. Also, with the battery

removed, was getting about the same voltage from the UPS at the terminals where the battery connects

so I assume the charging circuit was operational so no idea why the old UPS was indicating NO

charge in the battery other than some kind of internal failure with the unit.

 

I'll be keeping a close watch at the charge level of the new UPS.

I'd appreciate any insight as to what should be considered "normal" for this new UPS (BN1500M2)

with regards to how long it should take to reach full charge after a minor power problem (2 minutes or less).

Thanks for reading.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:49 PM . Last Modified: ‎2024-03-26 02:53 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:49 PM . Last Modified: ‎2024-03-26 02:53 AM

So, just an update:

Day 3 now of having the new UPS, and it is FINALLY showing 100% charge.

According to the specs in the owner's manual, the battery should FULLY CHARGE in 16 hours.

I have a 30 day return window at Best Buy, and am really curious if this seems normal.

Granted, over the 11 years I have owned my BX 1500G I never really paid too close attention

to the charge level, but 2 to 3 days seems a bit excessive for a brand new UPS to fully charge,

especially when the charge level STARTED at around 97%.

I'd consider ordering a new battery cartridge for my BX 1500G, but 2 things:

1) The unit is 11 years old and well past it's warranty

2) I immediately pulled the battery out at the first sign of trouble and checked it with

a volt meter, and was getting around 26.5vdc so to me, that seems about right. Also, with the battery

removed, was getting about the same voltage from the UPS at the terminals where the battery connects

so I assume the charging circuit was operational so no idea why the old UPS was indicating NO

charge in the battery other than some kind of internal failure with the unit.

 

I'll be keeping a close watch at the charge level of the new UPS.

I'd appreciate any insight as to what should be considered "normal" for this new UPS (BN1500M2)

with regards to how long it should take to reach full charge after a minor power problem (2 minutes or less).

Thanks for reading.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore