Back-UPS 350 beeps, then my PC shuts off but the monitors stay on

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS 350 beeps, then my PC shuts off but the monitors stay on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
9
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

Back-UPS 350 beeps, then my PC shuts off but the monitors stay on

I have PowerChute installed, but it reports no sort of incident regarding power. My PC just shuts down, though I do hear a beep at the UPS. When this first happened, it was giving off a continuous squeal and had to be reset. I adjusted the sensitivity to LOW in PowerChute, and now it just lets it shut down with a single beep.

My two monitors are on the second and third battery-backed outlets, but they stay on.

So is this just my PC shutting down on it's own, or is the backup faulty?

I have used this UPS since it was purchased new in 2011, but it's only been on this particular PC since last winter. It has always supported two monitors, and a few peripherals on the surge protected circuit.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

I have PowerChute installed, but it reports no sort of incident regarding power. My PC just shuts down, though I do hear a beep at the UPS. When this first happened, it was giving off a continuous squeal and had to be reset. I adjusted the sensitivity to LOW in PowerChute, and now it just lets it shut down with a single beep.

My two monitors are on the second and third battery-backed outlets, but they stay on.

So is this just my PC shutting down on it's own, or is the backup faulty?

I have used this UPS since it was purchased new in 2011, but it's only been on this particular PC since last winter. It has always supported two monitors, and a few peripherals on the surge protected circuit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

The UPS do have two sets of outlets, Surge Only and Battery Backedup outlet.  Make sure that critical equipment goes on the battery backedup outlet.  Also, the PC that has been shutdown shouldn't cause the UPS to beep.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

Yes, as I was describing, I have kept the monitors and the PC on those three batter-backed outlets. The PC has been in the one which could be considered "special", in that it is slightly separated from the other two (the one to the left). I was speculating it might be a circuit unto itself, as well as backed by the battery. I will experiment further and see if anything else gets shut off in that socket. Currently nothing is plugged into it, so I will test a single monitor and see what happens.

The beep happens at exactly the moment it shuts off the PC.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

What if you remove the PC and just leave the monitor attached on your UPS?  Would it still beep?  If it does, what would happen on the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

There may be something more afoot than an old battery, yes, but I have an old battery nonetheless. If it continues to fail after that, I will move to another brand.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

Since my last response a week ago, I have had only the two monitors on the battery side of this UPS. Just a few minutes ago, they both went off and the unit started beeping. A 1-2 second sound followed by continuous short beeps. This continues until you power off the unit. It wouldn't run two monitors, but it is now running one.

Does this indicate the battery needs replacement, or should I just abandon this thing for a new one?

Unfortunately, I uninstalled the PowerChute application, so I can't see what was happened on the unit side.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

Have you tried a pull plug test at all (pull the plug yourself and see what happens to simulate an outage)? Sometimes I find these units so simple that they are difficult to deal with laughing

Anyway, do you see any LEDs with the beeping?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

That's an interesting idea, Angela N. I just tried it. There was a single beep, the green LED stayed on (it has in past tragedies, as well - to answer your question), then 4 short beeps, then just continuous power to my monitors. I plugged it back in, and it seemed to reset itself. Is that what I should have expected?

I have ordered an OEM replacement battery already this past weekend, just in case that's the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

Well, we were just trying to simulate a power failure. It seems like it acted normally during your simulation so I don't see why it would not during a normal power failure (if that is even what happened during the last scenario).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

0 Likes
0
1596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:30 PM . Last Modified: ‎2024-03-21 12:50 AM

I have PowerChute installed, but it reports no sort of incident regarding power. My PC just shuts down, though I do hear a beep at the UPS. When this first happened, it was giving off a continuous squeal and had to be reset. I adjusted the sensitivity to LOW in PowerChute, and now it just lets it shut down with a single beep.

My two monitors are on the second and third battery-backed outlets, but they stay on.

So is this just my PC shutting down on it's own, or is the backup faulty?

I have used this UPS since it was purchased new in 2011, but it's only been on this particular PC since last winter. It has always supported two monitors, and a few peripherals on the surge protected circuit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore