Back-UPA ES 750 clicking under low load

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPA ES 750 clicking under low load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
6
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

Back-UPA ES 750 clicking under low load

I have a Back-UPS ES 750. Recently it has started clicking on and off every 10 seconds or so under certain conditions. It only seems to happen when the computer has switched off the display because it has been idle. If I do something on the computer to make the display come back on, the clicking stops. If I put the computer to sleep, the clicking stops.

I have PowerChute 2.2 and on the Performance page, it shows no unit switches at all, and when I look at the voltage on the Current Status page it doesn't vary more than from 119 to 121 volts. I have set the sensitivity to Low, but that didn't seem to really help. The Self-Test passed.

Any ideas what's going on?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

Thanks for the reply.

The model # is BE750G. Serial #: 4B0751P40002

It's not when it goes into standby or hibernate, just when the windows power settings kick in to shut off the display when the computer is idle. No daisy chain. I have a laptop with a docking station and a monitor plugged directly into the UPS, which is plugged into the wall outlet. I also have a phone, router, and cable modem plugged into the UPS, but no printer.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Thanks a lot for your help. If leaving the master feature off fixes it I will probably just leave it at that, at least for now, since I wasn't using that feature anyway.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

Do you have an exact model and serial # on the UPS? This would be on a white barcode on the bottom/side of the unit.

When your computer shuts off your display, does this coincide with the computer going into standby or hibernate? Also, is there any daisy chaining of power connections to the load (surge protector, etc.). Any printers plugged into the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

0 Likes
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:59 AM . Last Modified: ‎2024-03-22 02:56 AM

Thanks for the reply.

The model # is BE750G. Serial #: 4B0751P40002

It's not when it goes into standby or hibernate, just when the windows power settings kick in to shut off the display when the computer is idle. No daisy chain. I have a laptop with a docking station and a monitor plugged directly into the UPS, which is plugged into the wall outlet. I also have a phone, router, and cable modem plugged into the UPS, but no printer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Has the site wiring fault LED been on at any time on the UPS? What if you turn the monitor off manually instead of let Windows turn it off?

Have/can you try a different outlet?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Thanks a lot for your help. If leaving the master feature off fixes it I will probably just leave it at that, at least for now, since I wasn't using that feature anyway.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

I have not seen the wiring fault light come on. I have tried turning off the monitor manually to see if it would happen, but it didn't.

In fact, it doesn't happen all the time. It didn't happen at all yesterday (of course) though it was happening every day for a while before yesterday. It definitely only happens when the computer has been idle for a while, and I can definitely stop it from happening by waking the computer up or shutting it down.

Unfortunately, trying a different outlet would involve rearranging my office.

It just occurred to me that I turned off the "Master Enable" setting on the UPS yesterday. Could it be the master switch that is clicking on and off? My computer is a laptop with a docking station, and maybe when its display is off it falls below some threshold of power consumption that causes the master switch to cycle on and off. Or the laptop could be cycling between charging and not charging, which could be causing the master switch to cycle on and off. That must be what's going on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

If you turned off the master outlet feature on the UPS yesterday, and it hasn't happened at all today (assuming that is correct), then yes that is rather telling. It's likely the current threshold that the unit is set at for controlling the outlets is being hit, and then clearing, and the relay is making the noise when this happens.

Use this link to see the manual for the unit, which includes how to change the threshold. See if changing the threshold allows the unit to work with the master outlet feature on. Otherwise you may need to keep it off:

[http://www.apcmedia.com/salestools/KBOK-766PMZ_R2_EN.pdf]

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore