Replaced battery but light still on and beeps after reset - SC1500

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Replaced battery but light still on and beeps after reset - SC1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
20
21461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Replaced battery but light still on and beeps after reset - SC1500

I have a SC1500 tower, and have just replaced the battery (old batteries were from 12/2006). The battery replace light had come on last week and it was beeping every 5 hours. I ordered replacement batteries and have done a hot swap, but now, even after a POST, the replace battery light stays on and the unit beeps every ~2 secs for about ~3 secs.

I unplugged the new battery, plugged in the old, and did a POST, and the replace battery light turns off, and appears everything is fine. (Hmm, why didn't I try that before I ordered new batteries). Plug back in the new batteries and do a POST, and it keeps beeping and the replace battery light STILL on. Do the new batteries need to be charged?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

I have a SC1500 tower, and have just replaced the battery (old batteries were from 12/2006). The battery replace light had come on last week and it was beeping every 5 hours. I ordered replacement batteries and have done a hot swap, but now, even after a POST, the replace battery light stays on and the unit beeps every ~2 secs for about ~3 secs.

I unplugged the new battery, plugged in the old, and did a POST, and the replace battery light turns off, and appears everything is fine. (Hmm, why didn't I try that before I ordered new batteries). Plug back in the new batteries and do a POST, and it keeps beeping and the replace battery light STILL on. Do the new batteries need to be charged?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Hello Mary,

To start with, did you replace it with an APC battery? Do you have an APC software (PowerChute Business Edition) installed on your computer? If you do, have you tried updating the battery replacement date on it?

If it is an APC battery, can you tell us what is the serial number on it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

The battery was ordered from PC Connection, and appears to be a genuine APC battery. The box is from APC, the battery is stamped with APC logos and there are stickers declaring the battery Genuine APC, there is also a return address sticker in the box for recycling. The model and serial number are RBC59, 3A0935X01914. I have not installed the PowerChute software on the computer to which the SC1500 is attached.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

If your IT deparment would allow it, I suggest that we install PowerChute Business Edition on one of your machines and then let us view the event and data logs on it to see what is going on with the UPS. Also after installing it, let us update the Last Battery Replacement date on it.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Not a problem, I have a CD with PowerChute Business Edition Basic, from 2005. Use that, or is there another version I should be using - how do you want to proceed?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

I highly recommend that you download our PowerChute Business Edition 8.0.1 - Single Node Agent from our website and then install it on your machine. Please check our [PCBE Compatibility Chart|http://www.apcmedia.com/salestools/ASTE-6Z5QEV_R13_EN.pdf] to ensure that your operating system is supported.

Once you have installed the Agent, please login on the web interface and check the battery replacement date. Click on the Smart-UPS menu and then Configure to view the Battery Replacement option.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

I downloaded and installed PCBE 8.0.1, and have connected to SC1500. Changing the battery replacement date did not do anything after plugging in the new battery. However, the POST test message says it failed due to overload (although the overload light never came on). When I plug back in the old battery, the POST test succeeds. Both batteries report a voltage of 26.8 volts. It doesn't seem to change from the old to the new.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Are the batteries bad? Should I return them?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

Sorry for the late reply, would it be possible for you to paste the event logs captured by PowerChute software?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

I'm not sure if you have done this already but your response is greatly appreciated. After installing the new battery, was it left connected for at least 24 hours to fully recharge? Have you done a self-test after charging the new battery for a day? If you have not done this already please follow the steps outlined below.

+ Install the new battery and let it charge for 24 hours.
+ After 24 hours, press and hold the Test(On/Off) button of the UPS until the unit does a self-test. This can also be done by using our software.
+ Please observe the unit's behavior while you are doing a self-test and then paste the event logs of PowerChute here.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

I have not left the new battery plugged in for 24 hours yet. I will do that before I leave tonight, as it beeps for 2 seconds, pauses, beeps 2 seconds, continously, and I don't think too many people want to hear that all afternoon. When I did plug in the new battery, the Replace Battery light was flashing. I will paste the event log here in 24 hours. Thanks for your help so far.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

Thank you for giving us an update. If after 24 hours of charging the new battery and you have done what I've told you above and the SC1500 still has the flashing replace battery the UPS is not detecting the new battery. A flashing replace battery LED indicator on a UPS is what do we call as a Battery Disconnect issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

Good day Mary,

I already requested for a replacement for your faulty battery. Please feel free to contact us if you have any problems.

JonPro

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

So, I left the battery plugged in for 24 hours. It just kept beeping and the replace battery light is still flashing. I have a second SC1500, and I plugged the battery into that one. It too just kept beeping and the replace battery light kept flashing. The self-test reported that no battery was detected. I presume it is a bad battery and I should return it to PC Connection?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Yes, that is correct, actually, I do not know that the batteries ever charged since the replace battery light stayed on and the SC1500 continued to beep the whole time the new battery pack was plugged in. The old batteries are working fine.

Message was edited by: mmhst

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Mary,

Thank you very much for getting back to us. Based from the test that you have conducted and the results that we have gathered, it just confirms that the battery that you have there are faulty. I will be more than happy to send a replacement battery if you like. I will be e-mailing about the requirements before we send a replacement battery.

I apologize for the inconvenience this has caused you and appreciate all of your help.

Thanks,

JonPro

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Yes, that would be much appreciated. Would I just be sending the faulty new battery to the address on the UPS sticker (APC/Fortune Battery Disposal, NJ)?
The battery I have is the RBC59, 12v 7.2Ah.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

I just e-mailed you the details that we need in order to process the replacement. I used the e-mail that was on your profile, please reply back on that e-mail and we'll be putting in an order once it's all complete.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Many UPSs are unable to detect true overload from an under voltage caused by deteriorated batteries. When batteries deteriorate, two things can happen. Separately, or together.

Reduction in capacity: this results in a reduced run time.
Increase in internal resistance: this causes voltage to plummet under load and cause the UPS to think it was overloaded. If you don't get overload with no load(if you're able to remove load or try in another unloaded UPS) but overload indicator comes on well below the rated capacity, it's likely that you've a bad pack.

SLA batteries need maintenance in storage or they will be damaged. They can be stored for many years if they're given proper top off charge regularly. If allowed to sit in discharged conditions, they're done.

Vendors usually don't touch the batteries. I don't know how to read battery serial numbers, but APC should be able to tell you the manufacturing date. It should be no older than a year AT MOST. Otherwise, they likely died in the warehouse.

For future reference, don't buy from vendors with poor product turn over. If your particular type of battery doesn't have a good product turnover, order directly from APC, even if it may cost you a little more or find a dependable UPS service company to rebuild your pack with known fresh batteries.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 20
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

I have a SC1500 tower, and have just replaced the battery (old batteries were from 12/2006). The battery replace light had come on last week and it was beeping every 5 hours. I ordered replacement batteries and have done a hot swap, but now, even after a POST, the replace battery light stays on and the unit beeps every ~2 secs for about ~3 secs.

I unplugged the new battery, plugged in the old, and did a POST, and the replace battery light turns off, and appears everything is fine. (Hmm, why didn't I try that before I ordered new batteries). Plug back in the new batteries and do a POST, and it keeps beeping and the replace battery light STILL on. Do the new batteries need to be charged?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Hello Mary,

To start with, did you replace it with an APC battery? Do you have an APC software (PowerChute Business Edition) installed on your computer? If you do, have you tried updating the battery replacement date on it?

If it is an APC battery, can you tell us what is the serial number on it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

The battery was ordered from PC Connection, and appears to be a genuine APC battery. The box is from APC, the battery is stamped with APC logos and there are stickers declaring the battery Genuine APC, there is also a return address sticker in the box for recycling. The model and serial number are RBC59, 3A0935X01914. I have not installed the PowerChute software on the computer to which the SC1500 is attached.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

If your IT deparment would allow it, I suggest that we install PowerChute Business Edition on one of your machines and then let us view the event and data logs on it to see what is going on with the UPS. Also after installing it, let us update the Last Battery Replacement date on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Not a problem, I have a CD with PowerChute Business Edition Basic, from 2005. Use that, or is there another version I should be using - how do you want to proceed?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

I highly recommend that you download our PowerChute Business Edition 8.0.1 - Single Node Agent from our website and then install it on your machine. Please check our [PCBE Compatibility Chart|http://www.apcmedia.com/salestools/ASTE-6Z5QEV_R13_EN.pdf] to ensure that your operating system is supported.

Once you have installed the Agent, please login on the web interface and check the battery replacement date. Click on the Smart-UPS menu and then Configure to view the Battery Replacement option.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

I downloaded and installed PCBE 8.0.1, and have connected to SC1500. Changing the battery replacement date did not do anything after plugging in the new battery. However, the POST test message says it failed due to overload (although the overload light never came on). When I plug back in the old battery, the POST test succeeds. Both batteries report a voltage of 26.8 volts. It doesn't seem to change from the old to the new.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Are the batteries bad? Should I return them?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

Sorry for the late reply, would it be possible for you to paste the event logs captured by PowerChute software?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:00 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

I'm not sure if you have done this already but your response is greatly appreciated. After installing the new battery, was it left connected for at least 24 hours to fully recharge? Have you done a self-test after charging the new battery for a day? If you have not done this already please follow the steps outlined below.

+ Install the new battery and let it charge for 24 hours.
+ After 24 hours, press and hold the Test(On/Off) button of the UPS until the unit does a self-test. This can also be done by using our software.
+ Please observe the unit's behavior while you are doing a self-test and then paste the event logs of PowerChute here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

I have not left the new battery plugged in for 24 hours yet. I will do that before I leave tonight, as it beeps for 2 seconds, pauses, beeps 2 seconds, continously, and I don't think too many people want to hear that all afternoon. When I did plug in the new battery, the Replace Battery light was flashing. I will paste the event log here in 24 hours. Thanks for your help so far.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

Mary,

Thank you for giving us an update. If after 24 hours of charging the new battery and you have done what I've told you above and the SC1500 still has the flashing replace battery the UPS is not detecting the new battery. A flashing replace battery LED indicator on a UPS is what do we call as a Battery Disconnect issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

Good day Mary,

I already requested for a replacement for your faulty battery. Please feel free to contact us if you have any problems.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:55 AM

So, I left the battery plugged in for 24 hours. It just kept beeping and the replace battery light is still flashing. I have a second SC1500, and I plugged the battery into that one. It too just kept beeping and the replace battery light kept flashing. The self-test reported that no battery was detected. I presume it is a bad battery and I should return it to PC Connection?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Yes, that is correct, actually, I do not know that the batteries ever charged since the replace battery light stayed on and the SC1500 continued to beep the whole time the new battery pack was plugged in. The old batteries are working fine.

Message was edited by: mmhst

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Mary,

Thank you very much for getting back to us. Based from the test that you have conducted and the results that we have gathered, it just confirms that the battery that you have there are faulty. I will be more than happy to send a replacement battery if you like. I will be e-mailing about the requirements before we send a replacement battery.

I apologize for the inconvenience this has caused you and appreciate all of your help.

Thanks,

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Yes, that would be much appreciated. Would I just be sending the faulty new battery to the address on the UPS sticker (APC/Fortune Battery Disposal, NJ)?
The battery I have is the RBC59, 12v 7.2Ah.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

I just e-mailed you the details that we need in order to process the replacement. I used the e-mail that was on your profile, please reply back on that e-mail and we'll be putting in an order once it's all complete.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

Many UPSs are unable to detect true overload from an under voltage caused by deteriorated batteries. When batteries deteriorate, two things can happen. Separately, or together.

Reduction in capacity: this results in a reduced run time.
Increase in internal resistance: this causes voltage to plummet under load and cause the UPS to think it was overloaded. If you don't get overload with no load(if you're able to remove load or try in another unloaded UPS) but overload indicator comes on well below the rated capacity, it's likely that you've a bad pack.

SLA batteries need maintenance in storage or they will be damaged. They can be stored for many years if they're given proper top off charge regularly. If allowed to sit in discharged conditions, they're done.

Vendors usually don't touch the batteries. I don't know how to read battery serial numbers, but APC should be able to tell you the manufacturing date. It should be no older than a year AT MOST. Otherwise, they likely died in the warehouse.

For future reference, don't buy from vendors with poor product turn over. If your particular type of battery doesn't have a good product turnover, order directly from APC, even if it may cost you a little more or find a dependable UPS service company to rebuild your pack with known fresh batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

0 Likes
0
21457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:01 AM . Last Modified: ‎2024-03-22 02:54 AM

In addition to what JonPro said, could you please let us know the status of the Replace Battery Light? Is the Replace Battery Light flashing or Solid?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore