BX900R New - battery lasts 5 seconds

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX900R New - battery lasts 5 seconds
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

0 Likes
4
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

BX900R New - battery lasts 5 seconds

I just bought a BS 900 for my HDTV and cable box. After charging the battery for 18 hours and plugging in the equipment, I pulled the AC plug from the XS 900 input source and the battery powered the equipment for about 5 seconds and then shut down. This is not right. The equipment plugged into the unit to run off battery is approximately 270 watts, roughly a half load. The TV is 240 watts and the cable box about 25-30 watts

When I look at PowerChute is says the load is 248 watts and has 13 minutes of battery time.

If I take the TV off of the UPS and then unplug the source input the battery does stay on. It is only with the 240 watt TV pugged in that it shuts down shortly after it goes to backup.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

0 Likes
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

Thanks,

I exchanged the unit and the new one works fine. I actually don't care to power the HDTV from and UPS. My goal was twofold; 1) I live in Florida and during the rainy season we have a lot or short power outages and power surges. I wanted some extra protection for the new TV beyond what a standard surge protector offers. 2) The cable box has to reboot when power goes off. 98% of the outages are a few seconds and 1% more are less than 5 minutes. I tried to size the UPS for this 99% or the problem.

All seems well with the new one. I ran the TV and cable box for 13 minutes off the battery last night.

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

0 Likes
0
1334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

I just bought a BS 900 for my HDTV and cable box. After charging the battery for 18 hours and plugging in the equipment, I pulled the AC plug from the XS 900 input source and the battery powered the equipment for about 5 seconds and then shut down. This is not right. The equipment plugged into the unit to run off battery is approximately 270 watts, roughly a half load. The TV is 240 watts and the cable box about 25-30 watts

When I look at PowerChute is says the load is 248 watts and has 13 minutes of battery time.

If I take the TV off of the UPS and then unplug the source input the battery does stay on. It is only with the 240 watt TV pugged in that it shuts down shortly after it goes to backup.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

0 Likes
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

I did some more testing. With only the cable box(about 23-30 watts) plugged in I pulled the plug on the input AC to the BX900. The batteries power that unit for about 90 seconds and then shut down. What happened next is even more alarming. When I plugged the AC in again the yellow light came on, the green light did not, power resumed to the cable box and then the power to the cable box starting recycling on and then off. The yellow battery light went on and off too with these cycles. After about 5 times I shut it off and power back up and the green light came on and it seems to be normal.

These power cycles are about the worst thing you can do to electronics. Needless to say I have about 4 hours of weekend time into something that I should be able to plug in and run without ever reading any instructions.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

0 Likes
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

With regards to an HDTV being powered by a Back-UPS, I will only say that there is an APC line of A/V UPS's and surge filterers which do more than just a BX900R can for your equipment.

However, pertaining to your second setup, it seems that there is an inrush current upon transfer to battery and the load is increasing, which is decreasing the runtime, causing less than desired runtime from the UPS.

As far as plugging in only a 30W load and it powering off after 90 seconds, that's normal. APC Back-UPS are designed to have at least a load of 50W attached to the UPS, or it sense that it's not really powering anything while on battery, and will eventually turn itself off. If you're looking to power small watt consuming devices on battery, you're going to look at Smart-UPS for that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:53 PM . Last Modified: ‎2024-03-21 03:21 AM

Thanks,

I exchanged the unit and the new one works fine. I actually don't care to power the HDTV from and UPS. My goal was twofold; 1) I live in Florida and during the rainy season we have a lot or short power outages and power surges. I wanted some extra protection for the new TV beyond what a standard surge protector offers. 2) The cable box has to reboot when power goes off. 98% of the outages are a few seconds and 1% more are less than 5 minutes. I tried to size the UPS for this 99% or the problem.

All seems well with the new one. I ran the TV and cable box for 13 minutes off the battery last night.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore