Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-26 04:15 AM
Hey guys, I am new to this forum so pardon me if I am not aware of some rules.
Back to the topic, I have BX650LI-MS backup UPS. It is around 6months old, for the first 4 months it was running normally. However this 2 last month, every time power goes out (happens at least once per 2 weeks), my ups would only provide power for about 1-3mins then it will start beeping fast and shutdown. Another thing to note is that before it beeps normally every few minutes, now it doesn't. It isn't overloaded since I have only one low-end desktop plugged into it. I also tried leaving it turned on/off before sleep to test if that affects its charging behavior. You guys got any ideas? Its a pretty important topic to me since I am losing my documents/projects due to small time window i have to save.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-26 04:15 AM
Hi,
Sorry for the delayed reply. If the load is low it should not drop as you indicate. You should contact local support for assistance. They will required you to be with the unit to perform a few troubleshooting steps. You will find local support information on APC.com / Support.
Again, sorry for the delayed reply.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-26 04:15 AM
Hi,
Sorry for the delayed reply. If the load is low it should not drop as you indicate. You should contact local support for assistance. They will required you to be with the unit to perform a few troubleshooting steps. You will find local support information on APC.com / Support.
Again, sorry for the delayed reply.