BX1600MI-MS USB Connection Unstable

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1600MI-MS USB Connection Unstable
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All
Related Products
product field
Schneider Electric
Smart-UPS
product field
Schneider Electric
Back-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Alberos
Crewman Alberos
Crewman

Posted: ‎2024-11-07 06:49 PM

0 Likes
7
1038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-07 06:49 PM

BX1600MI-MS USB Connection Unstable

Hi,

 

First of all, I'm a home user not business.

 

I have a BX1600MI-MS UPS and its USB connection has been acting for a while now. The connection to PC will keep randomly dropout and then reconnect again. I already contacted APC and they already replaced my unit with a new one but the problem still here. It especially bad when things heat up (I played game, PC draw more load, etc. The UPS is no way near its limit btw, the load is only about 500W and this is 900W model, according to the box anyway.)

 

Here is my setup:

The USB cable from UPS is connected to USB hub (can be powered) that run into USB extension then finally into the back of the PC. Overall cable length is about 4-5 meters. My PC is on the other side of the desk and the UPS cannot physically be in the location that the included cable will reach the back of the PC. There is no (suitable) power socket there. And of course, I can't move my PC to the same side as UPS as the glass side will be on the left facing away from me. I paid for pretty RGB so I want to see it.... Also I never have any problem with any of the USB devices connect to the hubs in this setup.

 

What I already tried:

- Contacting support and they already replace mine with a new unit.

- Connect the power source to my USB hub.

- Try 4 different cables, 2 randomly found in my house, 1 a new one, and 1 the included one. (still connected to the same hub).

- Try different hub and different USB port on each hub. (I have 2 on my desk, connected to different USB port on PC).

- Uninstall and reinstall PowerChute Serial Shutdown.

 

What I think of:

- Will purchasing any of those "5m active USB cable" and run that directly to the back of my PC fixed it?

- Can I use power bar with surge protection on the UPS power lead? So I can move the UPS to the PC side. The manual said not to do it and only connect directly to the wall.

 

Again, please keep in mind that I cannot get the UPS to be on the same side as my PC. As there is no (suitable) power socket there. The one on that side doesn't have proper ground and it will shock me every time I touch my PC or anything metal connected to it. Speaking of good home electrical code right there...

 

Thanks

Labels
  • Labels:
  • Home & Office - Accessories
  • Home & Office - UPS & Software
  • Tags:
  • english
  • USB Connection
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Spock Teken
Spock

Posted: ‎2024-11-08 07:57 AM

0 Likes
4
1015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-08 07:57 AM

Take a long extension cord so you can move the UPS closer to the PC. Use the supplied USB cable and connect directly to both systems.

 

What happens?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

Alberos
Crewman Alberos
Crewman

Posted: ‎2024-11-08 09:21 PM

In response to Teken
0 Likes
3
966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-08 09:21 PM

Well, i don't have a plain extension cord. I only have power stip (with an R) with surge protection. Can I use that? It would be ideal if I don't have to move the UPS. As I will run into 3 more cable that I need to extend to reach the UPS. But I could move it temporarily just to see if it fixes it. Assuming the power stip with surge protection is ok to use of course.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-11-11 04:15 AM

In response to Alberos
0 Likes
2
964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-11 04:15 AM

Yes, we are only extending the power cord temporarily to see how the two systems behave. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Alberos
Crewman Alberos
Crewman

Posted: ‎2024-11-16 03:12 AM

In response to Teken
0 Likes
1
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-16 03:12 AM

Finally I'm able to test. So I move the unit today and use the supplied cable and.... nope, it's still dropping out that USB connection. Hasn't take long at all for it to dropout. This is the best case scenario, supplied cable connected directly to a USB 3.2 port on the motherboard at the back of the PC. So... what's my next plan here, the unit was already changed by APC support btw.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-11-18 03:21 AM

In response to Alberos
0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-18 03:21 AM

The possibilities have been narrowed down to the computer OS or PCSS.

 

Uninstall PCSS software and install PCPE instead to see the results. More than likely it’s the computer going into sleep / hibernate mode which is common.

 

The more likely scenario is the power save feature in Windows. Disable all power save features for the USB, SSD, CPU.

 

What happens?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

Alberos
Crewman Alberos
Crewman

Posted: ‎2024-12-05 07:47 PM . Last Modified: ‎2024-12-05 11:15 PM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 07:47 PM . Last Modified: ‎2024-12-05 11:15 PM

Hi, I haven't try your suggestion yet, haven't have to opportunity to move everything again. It's quite an inconvenience to move the UPS to be able to use the included cable. However, I did try 2 out of 3 things from your suggestion, installing PCPE instead of PCSS and disable USB selective suspension (or whatever it called) in Windows power setting. The power plan was already set to Balanced too. It still disconnecting, the problem is still here. I know this is not the good test as I still using those same long + hub + extension setup.

 

Before I finally has opportunity to move the UPS again, could you list a bunch of thing for me to try? So I don't have to move the unit often, as leaving it in that setup is also an inconvenience.... Sorry!

Reply

Link copied. Please paste this link to share this article on your social media post.

Alberos
Crewman Alberos
Crewman

Posted: ‎2025-01-10 09:12 PM

0 Likes
0
586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-10 09:12 PM

OK, just an update. Look like the problem is either on my Windows setup or the UPS flaw itself. I finally try the best case setup: included cable, both old PCPE and PCSS, USB selective suspension disabled as well as 'allow pc to turn of this device' unchecked in device manager. Still disconnecting.

 

I won't wipe everything and reinstall Windows just for this little feature, so might have to leave everyone on cliffhanger. I will contact the tech guy at tech support department locally again and share my testing to see what they have to say.

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of