BR1500S Lock‑Up (Green LED On, LCD Blank, No Output) – Firmware 952.e4 .D

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1500S Lock‑Up (Green LED On, LCD Blank, No Output) – Firmware 952.e4 .D
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
WildBillTX
Crewman WildBillTX
Crewman

Posted: ‎2025-08-02 06:42 AM

0 Likes
7
404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-02 06:42 AM

BR1500S Lock‑Up (Green LED On, LCD Blank, No Output) – Firmware 952.e4 .D

Yesterday I had a serious lock‑up issue with my Back‑UPS Pro BR1500S.

Details:

  • Model: BR1500S
  • UPS Firmware: 952.e4 .D
  • Display Firmware: 01.01a (1201‑19)
  • Battery: less than 1 year old
  • Environment: air‑conditioned, surge‑protected
  • Unit passes self‑test

Problem:
The UPS stopped delivering power to all outlets. Interestingly, this occurred during a routine monthly test of our Generac whole-house generator. During this test, the generator powers on and delivers power to the entire house for 30 minutes. At a particular moment during the test yesterday, our 3-ton air conditioner kicked on, an event that always has a momentary impact on voltage delivered to the house and to the UPS. However, the UPS has worked successfully in this scenario for months. Yesterday was the first time I’ve seen this lock-up. Symptoms:

  • The front green LED stayed on (as if everything was normal).
  • The LCD was blank and unresponsive.
  • None of the battery‑backed outlets had power.

Pressing the power button had no effect. Unplugging and re‑plugging wall power had no effect. The only way to restore output was to disconnect and reconnect the internal battery, which forced a reset.

Questions:

  1. Is there a firmware update newer than 952.e4 .D that resolves this lock‑up condition?
  2. If not, is APC treating this as a known issue (warranty replacement, etc.)?

Kind Regards

Wild Bill in Texas

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2025-08-05 04:23 AM

0 Likes
6
403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-05 04:23 AM

There is no firmware available for any APC Back-UPS that an end user can obtain and load. This must be done at the factory / repair facility.

 

Please upload the following logs from PCPE / PCSS for review: Event, Data, UPS

 

In the interim perform the following test and report back the results. Remove AC Mains from the wall and report back what happens.

 

Does the unit remain operational and if so how long does it run for in minutes. Compare this to the APC Runtime Calculator.

 

If the system turns off immediately the RBC needs to be replaced as it’s end of life.

 

Lastly provide the serial number of the unit and a photo of the RBC showing the production date of the cell.

 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

WildBillTX
Crewman WildBillTX
Crewman

Posted: ‎2025-08-05 12:20 PM

In response to Teken
0 Likes
5
388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-05 12:20 PM

Unfortunately I did not have powerchute configured for this UPS at the time of the issue.

I unplugged the UPS from the wall and it worked, supplying power to the attached equipment. I did not wait for it to drain the battery completely on this trial.

 

I searched for and did not locate a UPS runtime calculator for my particular model and load. If you have some guidance as to where I can find such a calculator, I would be happy to try it. In the meantime, can I just use the estimated runtime that gets displayed on the front panel?

 

I believe the serial number for the UPS itself is 4B2044P44787. I am attaching a photo of the batteries. I believe this date code indicates that one of the two cells was manufactured in April 2023 and the other in August 2023. But I’m no expert in interpreting these codes.

 

IMG_4006.jpeg

 

I located the record of my purchase of this UPS. The purchase date was July 2024

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-08-06 03:44 AM

In response to WildBillTX
0 Likes
4
386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-06 03:44 AM

You can obtain some information via the LCD to see the last ten faults / errors. Please take the time to connect the unit to a computer running Power Chute Software so more information can be obtained during the next event.

 

Please upload a photo of the battery which shows the production sticker. The image you provided is not the production date.

 

Runtime: The LCD provides only an estimate as to runtime. If the system was running for at least 10-15 minutes with a moderate load that’s fine for now.

 

The grid down test was to simply verify on the extreme side if the RBC was EOL. If so the system would have immediately dropped the load and turned off which didn’t happen here.

 

I would suggest you contact APC Technical Support if you believe the unit is faulty or wait to see the next generator self test to see how the unit behaves and engage the AC to replicate the same conditions.

 

If you decide to contact APC Technical Support please have the serial number, receipt, and brief description of the problem.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

WildBillTX
Crewman WildBillTX
Crewman

Posted: ‎2025-08-06 04:39 AM

In response to Teken
0 Likes
3
373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-06 04:39 AM

IMG_4001.jpeg

This? Sorry I don’t know the lingo. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-08-07 07:08 AM . Last Modified: ‎2025-08-07 07:10 AM

In response to WildBillTX
0 Likes
2
369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-07 07:08 AM . Last Modified: ‎2025-08-07 07:10 AM

If this is the OEM CSB battery cell the production sticker indicates it’s from August 15, 2020.

 

The service life is approximately 2-5 years based on usage, temperature, and environmental conditions.

 

This specific cell is passed its useful service life and should be replaced. If you did in fact purchase this in July 2024 it’s obvious the hardware was sitting on the shelf for a long time before you bought it.

 

Contact APC Technical Support and provide them with the purchase receipt. They will send you a new RBC (Replacement Battery Cartridge) for your system.

 

NOTE: It’s imperative that you make clear you purchased the unit in July 2024 and show them proof (receipt). Otherwise they will simply go by the production serial number of the unit.

 

Which in your case is produced 2020, 44th week.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

WildBillTX
Crewman WildBillTX
Crewman

Posted: ‎2025-08-07 11:52 AM

In response to Teken
0 Likes
1
356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-07 11:52 AM

Thank you. I opened a ticket. As it turns out, the unit that I bought from an authorized reseller in July 2024 was manufactured in 2020. Go figure. At any rate, Support agreed to send me a replacement battery. If that doesn’t solve the problem, they will do a warranty replacement on the unit itself.

 

I appreciate your help with this!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-08-08 03:26 AM

In response to WildBillTX
0 Likes
0
352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-08 03:26 AM

That’s great to hear and please do follow up with the final outcome once the RBC has been replaced.

 

As a gentle reminder the following action items must be completed once the RBC has been replaced:

 

Battery: In Power Chute (PCPE / PCSS) update the battery installation date.

 

Self Test: Manually initiate a self test via LCD Menu / PCPE / PCSS and wait for it to pass & complete and return to 100%.

 

Battery Calibration: If this feature is available in Power Chute. Manually initiate this process with at least 30% attached load. Once complete allow the system to recharge the RBC back to 100% SOC (State of Charge).

 

Doing so will help the system reflect the correct operational runtime in both LCD Menu & Power Chute.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore